Discuss Old glow worm 30 ci combi in the Gas Safe Register Forum - Public Forum area at UKPlumbersForums.co.uk.

  1. Inverness

    Inverness Plumber GSR

    im reading the manual for this boiler but I don't understand what I need to adhieve for the flue gas anaylser? I know it requires 3.4m3/h on a gas rate test with dhw on full? I'm getting 2.7m3/h.
    Also how to i adhieve for low firing on this boiler?
     
  2. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    Don’t think you can on the old ci or cxi range. Think it is just within normal standards for high, unless it has the potentiometer on the back of pcb specifically for high and low? but I cannot remember off the top of my head and I am not at home to check for you mate. Did you -your 10% for the gas rate that you are allowed to?
    Sorry if this is a confusing message.
     
  3. Inverness

    Inverness Plumber GSR

    Yeah it's an old boiler and in the manual there's no word for adjusting from max to min. I don't understand about the 10% ? Thanks for your response.
     
  4. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    Gas rate allowance is normally the spot on figure -10% or + 5 % but you are still nowhere near the 3.4 you need

    Somebody may correct me on this. (Or in the manual there maybe a figure next to the gas rate box)
     
  5. Inverness

    Inverness Plumber GSR

    It only says 3.4 no tolerances. I got 2.7 but flue gas analyser reading was not too bad. It is a medium operating pressure gas meter.
     
  6. sammathias

    sammathias Plumber GSR

    The appliance is undergassed... What was the pressure at meter and appliance? Don't know about the boiler in question but probably a partial blockage?
     
    • Like Like x 1
  7. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    I would put money on undersized gas pipe myself but might as well be a blockage
     
    • Like Like x 1
    • Agree Agree x 1
  8. Inverness

    Inverness Plumber GSR

    4 meters of 22mm pipe that's runs up the wall then into gas boiler no other gas appliance. My gas ratio was .0014
     
    • Like Like x 1
  9. Last Plumber

    Last Plumber Plumber GSR

    Need pressures. W.P. at meter and at appliance as Sam said.
    You need to get in the habit of taking readings.
    It will make things a lot more obvious to you when trying to diagnose something.
     
    • Agree Agree x 1
  10. Inverness

    Inverness Plumber GSR

    Wp at meter 19mb
     
  11. Last Plumber

    Last Plumber Plumber GSR

    What is it at the appliance?
     
  12. Inverness

    Inverness Plumber GSR

  13. Last Plumber

    Last Plumber Plumber GSR

    The page you want is 32 of this book I think.
    Go to this Link.
     
  14. Bibbs118

    Bibbs118 GSR

    0.0014 is fine.
     
  15. jtsplumbing

    jtsplumbing Plumber GSR

    Get gas supplier out to adjust governor on meter may even be faulty
     