Messages
710
im reading the manual for this boiler but I don't understand what I need to adhieve for the flue gas anaylser? I know it requires 3.4m3/h on a gas rate test with dhw on full? I'm getting 2.7m3/h.
Also how to i adhieve for low firing on this boiler?
 
im reading the manual for this boiler but I don't understand what I need to adhieve for the flue gas anaylser? I know it requires 3.4m3/h on a gas rate test with dhw on full? I'm getting 2.7m3/h.
Also how to i adhieve for low firing on this boiler?
Don’t think you can on the old ci or cxi range. Think it is just within normal standards for high, unless it has the potentiometer on the back of pcb specifically for high and low? but I cannot remember off the top of my head and I am not at home to check for you mate. Did you -your 10% for the gas rate that you are allowed to?
Sorry if this is a confusing message.
 
Yeah it's an old boiler and in the manual there's no word for adjusting from max to min. I don't understand about the 10% ? Thanks for your response.
 
Gas rate allowance is normally the spot on figure -10% or + 5 % but you are still nowhere near the 3.4 you need

Somebody may correct me on this. (Or in the manual there maybe a figure next to the gas rate box)
 
It only says 3.4 no tolerances. I got 2.7 but flue gas analyser reading was not too bad. It is a medium operating pressure gas meter.
 
It only says 3.4 no tolerances. I got 2.7 but flue gas analyser reading was not too bad. It is a medium operating pressure gas meter.

The appliance is undergassed... What was the pressure at meter and appliance? Don't know about the boiler in question but probably a partial blockage?
 
4 meters of 22mm pipe that's runs up the wall then into gas boiler no other gas appliance. My gas ratio was .0014
 
4 meters of 22mm pipe that's runs up the wall then into gas boiler no other gas appliance. My gas ratio was .0014
Need pressures. W.P. at meter and at appliance as Sam said.
You need to get in the habit of taking readings.
It will make things a lot more obvious to you when trying to diagnose something.
 
Status
Not open for further replies.

Reply to Old glow worm 30 ci combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi I have a Glow-worm back boiler which is giving me grief (I would have upgraded it by now but its a listed building and there's issues with...
Replies
6
Views
492
The flue for a glow worm micron 30ff is apparently obsolete but there must be other flues that would fit it surely, it's just a standard 100mm...
Replies
7
Views
628
My daughter lives alone in a 3 bed semi in the west country. The house is 20 years old. The central heating and hot water are provided from a...
Replies
1
Views
180
P
Does anyone know where I can find the decibel rating for the British Gas 330+ boiler? I'm looking to get it replaced and wanted to compare it...
Replies
1
Views
915
I am looking for some basic advice please My house is on two floors, approx 240m2 and a spacious loft with good headroom and access. Glow Worm...
Replies
4
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock