D

Dickie

Does anyone fit a lot of combis to old open vented systems and can they provide a copy of their 'waiver' in respect of 'Our price will not include the repairs that maybe required to the existing system with the increased pressure, etc, etc....'
Thanks chaps.
 
No guarantee can be given for existing pipework and fittings.
 
Agree with SimonG, I pressure test first to 1.5-2.0 bar, you can not guarantee work that you have not installed though.
 
I would always give a quote for full heating, then a quote for boiler change only, if doing full system all workmansip, PIPEWORK and material is guaranteed for one year
If boiler swap only " a system pressure test on existing will be carried out at 2bar, if would be reasonable to expect a sound system not to fail at this pressure therefore any failure of the existing system and subsequent repair due to the test will not be covered by quote or guarantee and repairs will br chargeable, only material supplied and fitted by me is covered by my guarantee, and no existing PIPEWORK , valves or radiators etc is covered in any way if as a result of increased system pressure ( which is normal and expected) there is a leak, please note that any subsequent structural or fabric damage is not covered by either guarantee or PIL
Haha when you read it back it will put some customers off, but that's too bad, cause if its not written down and accepted they will not pay for extra work and expect you to pick up the tab for leaks later on, which will be electrician call out, joiner and painter
 
Last edited by a moderator:
Thanks guys, but I was looking for T&Cs in that respect.

No guarantee can be given for existing pipework and fittings.

That is one of the standard terms in my terms and conditions.
 
Status
Not open for further replies.

Reply to Open vented system to sealed system Waiver. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
573
Hi all, We're looking to update our existing central heating setup and wanted to get a few more opinions. We currently have an open vented...
Replies
11
Views
1K
Hi guys, We have an open vented heating system and a Worcester Bosch greenstar boiler. Recently there is little to no heat getting to all...
Replies
2
Views
657
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
B
Context for issue: I'd like to start by saying I'd rather not read 100 "Hire a professional comments", I will do that when/if it comes to it, but...
Replies
0
Views
404
Butchy10
B
Back
Top