WaterTight

Esteemed
Plumber
Subscribed
Messages
5,439
But not together haha...

Couple of questions..

1. There's an overflow pipe run into a boss on a soil which has come loose. Not sure if right adaptor was used. What's the correct fitting to connect an overflow pipe to a soil pipe boss? The boss is already there, I just need to connect overflow to it.


2. I've fitted isolation valves (non full-bore) when swapping/adding rads to systems where the water is traditional vented pumped heating. I know you're not recommened to because of reduced flow but so far every time the rads have got hot with no probs. Done it about 4 times. Have I just been lucky or is it actually quite unlikely to actually cause a problem?
 
Overfow should NEVER be connected to a soil pipe but run outside. Very wrong - don't reconnect it but plug up the boss and do another arrangement.

If it is from a WC, replace the syphon with an internal overflow type.

You have been lucky. Use a freezing machine in future!
 
Hi, What if unvented tank is fited on 5th floor, do overflow still have to go outside?
 
not necessarily if there is a tundish to give visible view of flow from prv.
 
Thanks,
one more question
can I tee-ed 15mm pipe from presure relive valve and tempriture relieve valve before tundish and from tundish go in to 22mm copper (verticaly) for minimum 300mm then in to dry trap and in to 4" pipe?
 
Thanks,
one more question
can I tee-ed 15mm pipe from presure relive valve and tempriture relieve valve before tundish and from tundish go in to 22mm copper (verticaly) for minimum 300mm then in to dry trap and in to 4" pipe?

Yes, after tundish fit reducer and 1 1/4 hep trap in vertical position, by doing that and short of pipe and bend you will get 300mm, but only in push-fit not solvent and only internal stack.
 
Status
Not open for further replies.

Reply to Overflow and radiators. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have an opening on the 'manifold' (I think that's what its called) on my soil pipe. It appears to be a non-standard size - about 51mm...
Replies
9
Views
879
A
Hey, I'll start by saying I'll be getting a plumber out to do this but wanted some advice first. We're redoing our ground floor bathroom this year...
Replies
5
Views
965
Been researching as much as I can and think have a good gist about recommended waste pipe sizes, types of bends etc so now just looking to fit the...
Replies
3
Views
1K
Hi everyone, I have CH with a system boiler with a header tank and 8mm micro bore pipes to the radiators, fairly standard setup I guess. House is...
Replies
24
Views
3K
This post just for interest/comment so please only read if you have spare time. Following on from previous post soldering the elbow connection in...
Replies
2
Views
1K
Back
Top