Hello all, hoping someone could help me with this, Boiler pressure is 1.5 bar, but when we turn on UFH pressure drops to 1 bar. then when we turn off UFH, pressure on boiler goes back up to 1.5 bar?? any help much appreciated
 
With a sealed system and if the E.vessel is teed in just before the pump suction then the boiler pressure will/should rise by the pump head each time it starts so a 0.5bar, 5M rise might be normal.
Have you rads on the system as well?, if so watch the pressure if you switch them in and out with no UFH.
 
Last edited:

Reply to Pressure loss when UFH called for in the Water Underfloor Heating Advice area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
260
PSxxxxxx
P
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably...
Replies
1
Views
149
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
361
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
190
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
307
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock