P

Paul Thompson

Hi all,
I've just swapped over programmers from my defunct honeywell ST699 to their ST9400C. My system includes a V4073 mid position valve and an L641 Cylinder Stat.
The instructions showthe replacement wiring from one unit to the other which i have followed.
Problem! The CH, lights up on the programmer and the boiler fires up but although the Hot Water lights up on the programmer, it doesn't fire up the boiler? I've tried turning up the cylinder stat to induce the boiler to start but to no avail.
Any ideas?
Paul.
 
Hi all,
I've just swapped over programmers from my defunct honeywell ST699 to their ST9400C. My system includes a V4073 mid position valve and an L641 Cylinder Stat.
The instructions showthe replacement wiring from one unit to the other which i have followed.
Problem! The CH, lights up on the programmer and the boiler fires up but although the Hot Water lights up on the programmer, it doesn't fire up the boiler? I've tried turning up the cylinder stat to induce the boiler to start but to no avail.
Any ideas?
Paul.

Is there a wire at the 'Hot Water off' terminal on your new programmer?

It sounds like you've maybe wired it incorrectly mate. Did it fire for HW before you replaced the prog?
 
Mbear, thanks for the reply, The wire for the HW off on the ST699 was at terminal 7 and the new instructions say to wire this to terminal 1 on the ST9400 which i have done. It did fire on the old programmer (the old programmer was replaced because the timer functions went mad and i had to switch it manually)

Thanks for the reply Doitmyself,
The backplate has been replaced (part of the new ST9400) as they differ in size. What remains in my old ST699 on my desk is the link between 5 and 8 as you rightly point out it's not needed on the ST9400.
 
Last edited by a moderator:
Do u know how to fault find and trace voltage on ch systems?

Also do u have a fluke meter?

Try this...
turn power off and prove dead,
Remove the facia from the new prog,
get a spare piece of wire and strip bare at each end,
use this wire to wire the 'live terminal' together with the 'hw on terminal',
stand back and turn power on,

if boiler fires for hw then there may be a fault with the new prog unit or you've maybe not set it or wired it correctly bud
 
Last edited by a moderator:
Unfortunately not on both counts mbear. i'm wondering if the ST9400 is faulty? then again something else may have caused the ST699 to go awol?
 
Mmmm Stand back eh! what could happen? That looks like i'll be putting a live feed to the cylinder stat, is that what you meant?
 
Last edited by a moderator:
Mmmm Stand back eh! what could happen? That looks like i'll be putting a live feed to the cylinder stat, is that what you meant?

Nothing should happen, just meant the terminals will be exposed and live, basically don't touch. Safety first and all that

yeah, basically it's called 'linking out', it means u r taking the prog out of the equation. If it fires then u can be sure there's summit not quite right with the prog. U can link out lots of things in ch to prove if components are faulty or not
 
Nothing should happen, just meant the terminals will be exposed and live, basically don't touch. Safety first and all that

yeah, basically it's called 'linking out', it means u r taking the prog out of the equation. If it fires then u can be sure there's summit not quite right with the prog. U can link out lots of things in ch to prove if components are faulty or not

Thanks for the useful info I'll give it a go
 
Did you manage to fix it. I have same problem. Lights up, but no one home. :)
 
Status
Not open for further replies.

Reply to programmer swap no no hot water! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, I have an OSO Direct 210 hit water cylinder installed in my home, with 2 switches (on/off; and boost). The boiler is for hot water only...
Replies
6
Views
497
Heating and hot water is not working. Plenty of heating oil. I have replaced batteries in thermostat and it seems to be working ok, showing flame...
Replies
5
Views
368
My first thought when I heard this fault a combi boiler with hot water but no heating. Was a problem with the stat, controls not making the call...
Replies
0
Views
359
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
429
B
Issue with boiler short cycling in system with hot water tank. We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank...
Replies
10
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock