I have a job where I need to run 30 metres of 28 mm and 10 metres of 22mm copper tube. Now there is no gas hob in the place so I need to light the gas while purging. What right do you guys make up in this scenario. Cheers
 
+1 and what you feeding cant be much after 40m total

and a bunsen burner
 
sorry mutt, but i disagree!! probably wrong though!
whats the meter?
g4 i make it 0.04401m3

So to calculate the installation volume it is G4 metre 0.008 + 30 metres 28 mm 0.0162 + 10 metres 22mm 0.0032 + 10 % for fittings is 0.0301?

Have I made a mistake some where
 
So to calculate the installation volume it is G4 metre 0.008 + 30 metres 28 mm 0.0162 + 10 metres 22mm 0.0032 + 10 % for fittings is 0.0301?

Have I made a mistake some where

must be! 30mx28mm is 0.0387m3 & 10mx22mm is 0.01728m3 !!

according to the rays gas app...
30mx28mm + 10mx22mm not adding any fittings its 0.04401m3 or 0.04614m3 with fittings!!

think youve been hoping to do it in 10mm aint u? lol
 
must be!
according to the rays gas app...
30mx28mm + 10mx22mm not adding any fittings its 0.04401m3 or 0.04614m3 with fittings!!

you got a link to rays app?
 