I have a job where I need to run 30 metres of 28 mm and 10 metres of 22mm copper tube. Now there is no gas hob in the place so I need to light the gas while purging. What right do you guys make up in this scenario. Cheers
Discuss Purging long gas supply in the Plumbing Jobs | The Job-board area at PlumbersForums.net
are you in scope?
no bends eh?Sure, it is still domestic as it comes in at 0.03255
no bends eh?
no bends eh?
Only 6 fittings on the run
sorry mutt, but i disagree!! probably wrong though!
whats the meter?
g4 i make it 0.04401m3
So to calculate the installation volume it is G4 metre 0.008 + 30 metres 28 mm 0.0162 + 10 metres 22mm 0.0032 + 10 % for fittings is 0.0301?
Have I made a mistake some where
must be!
according to the rays gas app...
30mx28mm + 10mx22mm not adding any fittings its 0.04401m3 or 0.04614m3 with fittings!!
you got a link to rays app?