Was there anything to stop the secondary return going back to the cylinder ?
Just thinking it is strange to have a blending (tempering) valve on the outlet of an un-vented as they should be controlled by the stats. If it has been fitted to actually reduce the temperature of the HW flow to the fittings then the return could have been taken back into the cold supply to the valve, otherwise the return water to the cylinder would cool its stored temperature causing it to reheated. This HW would then be drawn out of the flow only to be blended back down by the cold, if that make sense. Very poor design, my guess is the return goes through the valve no (or very little) back to the cylinder.
Just thinking it is strange to have a blending (tempering) valve on the outlet of an un-vented as they should be controlled by the stats. If it has been fitted to actually reduce the temperature of the HW flow to the fittings then the return could have been taken back into the cold supply to the valve, otherwise the return water to the cylinder would cool its stored temperature causing it to reheated. This HW would then be drawn out of the flow only to be blended back down by the cold, if that make sense. Very poor design, my guess is the return goes through the valve no (or very little) back to the cylinder.