Discuss Replaced PRV and still leaking in the Plumbing Jobs | The Job-board area at PlumbersForums.net
the PRV has been replaced twice in the past few months and this seems to cure the leak temporarily, however the leak is now worse and is clearly caused by a different problem. The pressure gauge rises quickly upto 3 bars, (we release the pressure manually) but then when the heating/water is off (boiler not running) it loses pressure to zero whilst it’s off. there is an expansion tank already fitted, this was replaced approx 7 years ago. Does it sound like the expansion tank needs replacing or could it be something else?
Who fitted the replacement PRVs twice?
You need a heating installer to take a look at it all and also service the boiler, whatever boiler it is.
Note the expansion vessel is supposed to be serviced at each service and certainly will not function properly, if at all, unless it gets checked fairly frequently
When was the last time that the boiler was serviced? This should have been checked on the annual service if I’m honest.
First things first is the prv and expansion vessel inside the boiler? What boiler is it?
Any chance of a pic of the prv ?
Well yes but I suspect that OP is confused with regard to Safety devices on an unvented and those on the boiler
Photo of PRV
It’s a potterton boiler
Find the red Red expansion vessel
Yep sealed system
Red expansion tank needs looking at best get your boiler service guy to have a look at it
So the PRV in the airing cupboard for the heating, should be attached to or next to the red vessel in the garage. I ask again though. When was it last serviced?
Doesn’t need to be
Thank you for your replies
Just to clarify, it appears to be the red expansion tank? The one next to the boiler that has a problem? Not the one next to tank?
How do you know that?
Has it been all serviced?
Has the cylinder also been serviced?
Should be as close to the boiler as possible mate (shouldn’t it)
Doesn’t matter aslong as there’s no valves on the boiler / between the boiler and prv
I suppose if the pipes from boiler froze in severe weather (highly possible if boiler is in garage or an attic), then a remote prv could end up being isolated and no use
Should have a frost stat and that wouldn’t make any difference anyway as unless it’s inside the boiler would be the same
Think of a standard heat only boiler where’s the vent connection / tee normally in the airing cupboard
On this instance though Shaun. It makes no sense to put the PRV where they have when they have fitted the external vessel next to the boiler. They cannot use the excuse of not having an external wall. It’s a garage, it will have at least 1.:p:p
Just one more thing, the boiler has had all components completely replaced, all the PRVs and
The hot water tank expansion vessel have been changed in the last two years.
The only two things that have not been replaced in the past two years is the red expansion vessel next to boiler and the actually hot water tank itself, could it be the hot water tank itself gone wrong?
Unfortunately we cannot say. You will need an G3 registered engineer to tell you that.
Yes it could in theory as it is an old enamelled steel type cylinder which I bet has not had the anode replace. If the internal heat exchanger has rusted the higher pressure domestic water could be leaking into the heating water raising the pressure so the heating safety valve discharges at 3bar.
As per other, get a good G3 engineer in (& disconnect that filling loop as per Water Regs).
Yes it could in theory as it is an old enamelled steel type which I bet has not had the anode replace. If the heat exchanger has rusted the higher pressure domestic water could be leaking into the heating water. As per other get a good G3 engineer in (& disconnect that filling loop as per Water Regs).
The pressure in the heating doesn’t rise when off it drops.
I know what you are saying, but even on an open vented system, I always put a prv on the system, - and straight off the boiler pipes. Normally only oil systems, but also some gas.
If an open system feed and vent froze in the attic, the prv would be needed
and if the prv froze
Everything points to getting it checked out by a gas safe heating engineer, and perhaps a different one/firm who replaced the prvs. The parts have been replaced in the last 2 years but it doesn’t mean they don’t require checking - as per previous posts every service.
Then there would be no open pipe safety left.
But the boiler can likely be the last system area to freeze. Pipes leaving it in a garage are usually more vulnerable to freezing first, as would vent and feed in some roofspaces.
As you said, frost stat should save the boiler
Reply to Replaced PRV and still leaking in the Plumbing Jobs | The Job-board area at PlumbersForums.net
losing pressure
L
Hi, all. I have a leak problem behind the washing machine. It's a pipe that is leaking directly into a drain. It used to drip but now is leaking a...
Pritesh Patel
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Good evening, I'd like your opinion on something that is worrying me please: my landlady's plumber replaced the bottom/night element of my...
Hi, I have an unvented water heater which for some reason every year causes me issues. At the end of 2023 I noticed that the pressure valve...