Hi all,

In my new build I have 4 soil pipes that pop up at various walls on the ground floor. All pipes connect into a single pipe for the sewer.
One pipe will connect to a toilet on the first floor and also connect to the shower and sink waste. Another will connect for kitchen water waste and the others for future provisions.

For building regulations I understand that I need a vent.
My question: Do I need to vent in only one place - i.e. near the toilet or do I need to vent all pipes?

For the vent, how high does it need to vent?


Thanks,
Dave
 
OK, so I'll vent the one connected to the toilet (which is at a high point).

Regarding the Durgos, I understand they have to be placed on a vertical connection. Do they have to be a certain height and presumably these are OK to add on the first and ground floor?

Dave
 
The original distance was three foot above any opening into a building. I still use that and I wish the rest of the world would stick to what's in my head lol.

Minimum 3ft (900mm) in my head too. I still stick to that as well. Makes me cringe how many times I see a low level hopper T'd into a stack or a gutter downpipe put into a stack effectively making the height of the vent void and now venting at gutter level inches away from a bedroom window or venting out of the hopper at the side of a kitchen door etc..
 
To really get technical about the situation, you need to provide a plan of the drain runs, distances and pipe sizes.

There are regulations available about venting of soil pipes available.
As long as you follow the regulations, you shouldn't have a problem
 
My understanding of AAV's were to be fixture based
eg: You have a basin installed to a stack and you can't get the allowed distance from the vented stack to the fixture location.
So without running a vent from the fixture to atmosphere you could install an AAV.

I would never install an AAV at the top of a stack or on a branch drain that is picking up several fixtures.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Soil Pipe Vent Question" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
David Usher,
Last reply from
oz-plumber,
Replies
9
Views
4,242
Back
Top