Hi, i have been called to an unusual job for our company and was looking for some guidance. The spray booth is being heated by a gas burner fed from L.P.G cylinders. The burner will come on at high heat for a few seconds and then drop to a low burner pressure. I have spoke to the customer who tells me this is not normal and should come on at high flame until temp is reached and then regulate down. I have tried linking out the stat to which the burner will then be a continuous full burner, because it done this I assumed that this temp stat was faulty and ordered a replacement. I have since been back and this replacement is doing the same thing as the original. Any help would be appreciated.
 
Commercial mate

You got yours ?
 
A bit

Normally have a stat inside the paint booth etc you tested that ?
 
Have you checked the internal stat ?
 
20180518_134725[1].jpg
20180518_134725[1].jpg 20180518_134725[1].jpg
 
I have checked the stat which is checking the internal temperature of the spray/bake booth. It is located within a ceiling type void.
 
Does it stay on high burn when you bypass the spray booth stat ?

Looks like it could do with a decent service
 
Couple of question:
Is it just a 2 setting flame or continously variable between high and low?
You say linking the stat keeps it on high flame, what type of stat is it ? - just contacts or electronic.
Trying to figure out whether you have a PID controller or not
 
Status
Not open for further replies.

Reply to spray booth burner low burner pressure in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, whenever my Gloworm 18r is on even if I leave it on non-stop for 6 hours the flame symbol for the burner never switches off and the radiator icon never stops flashing implying the rads are calling for more heat, even though they're all red hot and have been for hours, is this a fault or just...
Replies
4
Views
329
I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts needed to operate it are now new. The symptoms indicated a broken/seized burner motor or oil pump. I wrongly assumed the motor so I ordered a new one only...
Replies
3
Views
727
I have a Grant Vortex Blue 26kw external oil boiler, installed less than 12 months ago. It's had intermittent non-starting problems resulting in multiple warranty visits, part replacements and eventually burner replacement. The replaced burner I discovered was a 'yellow flame' one, apparently...
Replies
5
Views
836
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not been serviced in a long time and oil filters were bunged up as was the nozzle. I decided to service it with hopes it was simple starving of fuel from...
Replies
1
Views
623
P
Hi All, I have replaced my existing Shaw and Mason chrome set with the Shaw and Mason forward bowl spindles/ Handles. I have kept the same tap or the water dispensing unit. The water pressure has reduced after I made the changes. I installed the original spindle back but same low pressure. If I...
Replies
0
Views
267
PRJSyd
P
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock