Evening all,
A regular customer of mine who has a beauty salon and a hairdressers shop adjoining each other and running off the same inlet water main has decided without getting advice to purchase the accumilator because of low water pressure apart from a structurel weight bearing issue the incoming mains is 15mm would i be right in saying this is inadequate
Thanks
 
Steve, I fit a lot of accumulator systems. To be effective they generally need to have a stored capacity of at least 200 litres and preferably 400litres. The later will deal will a poor flow rate on the recharge cycle.

In general terms ( domestic properties) aim to design for a pressure of 4.5bar with a flow of 30 lites / minute.

Avoid the approved pumps that “suck” from the mains. I work in the Thanes Water area, even with the WRAS pumps, once they realise one is installed they instal a restrictor ahead of the meter !

A final point, they really need to be installed on the ground floor - don’t be fooled by the Stuart Turner iboost solution - it is excellent in a plant room, but not in a kitchen cupboard ( unless you are hard of hearing!)

Hope this helps
 
Steve, I fit a lot of accumulator systems. To be effective they generally need to have a stored capacity of at least 200 litres and preferably 400litres. The later will deal will a poor flow rate on the recharge cycle.

In general terms ( domestic properties) aim to design for a pressure of 4.5bar with a flow of 30 lites / minute.

Avoid the approved pumps that “suck” from the mains. I work in the Thanes Water area, even with the WRAS pumps, once they realise one is installed they instal a restrictor ahead of the meter !

A final point, they really need to be installed on the ground floor - don’t be fooled by the Stuart Turner iboost solution - it is excellent in a plant room, but not in a kitchen cupboard ( unless you are hard of hearing!)

Hope this helps
Good advice thanks. The storage on this is 174 litre and the weight on the first floor will be 347kg . The usage is for hair washing mainly from instant hot water points so maybe 174 litre may be fine
 
whats the flow rate of the main now?
 
Steve,

If you can send me the pressures (static and dynamic) and flow rates, outlet heights et al - I am happy to give you an indicative design. If you also let me know the pump specification and elevation of the accumulator and outlets - I can give you expected flow rates and pressure.

It won’t be spot on - but I have a lot of empirical data as to how these units perform.

Without putting a negative slant on this topic, an M300sv is “up against it” at first floor level in a commercial property unless the incoming flow is greater than 10 litres/minute.

Stuart Turner in Henley are very responsive. In my experience, they don’t want their products installed in the wrong situations and are very keen to work with you to get the right solution.

In the Thames Water area low (crap) flows and pressures are a very common problem - they only want to be associated with success
 
Last edited:
Steve,

If you can send me the pressures (static and dynamic) and flow rates, outlet heights et al - I am happy to give you an indicative design. If you also let me know the pump specification and elevation of the accumulator and outlets - I can give you expected flow rates and pressure.

It won’t be spot on - but I have a lot of empirical data as to how these units perform.
Yes if that's ok. I need to wait until the salon landlords back to take a look. Thanks
 

Reply to Stuart Turner M300SV mainsboost in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi Everyone, For those who like a long read but I could rally do with some advice. Might be a bit long this. For background. A...
Replies
3
Views
322
Hello, I am renovating a small bathroom in an apartment on the 5th floor. Heating is electric, no gas or oil. I have four (related) questions...
Replies
1
Views
790
Hi all, looking to replace a Stuart Turner Pump No 10 which has died on me. The pump sits under the bathroom floor, where the well water supply...
Replies
0
Views
612
Hi there, Apologies for the mammoth post but my neighbours and I really need some advice... I recently purchased a flat that was built in 2016...
Replies
13
Views
2K
Hi, We have <2 bar coming into the house, sometimes as low as 1bar and on occasion .8bar. Thames Water been out, won't / can't do a thing. Not...
Replies
8
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock