Discuss System or Heat Only Boiler in the Central Heating Forum area at PlumbersForums.net
John.g
Subscribed
A (if) CH system has a very high head loss due to improperly sized pipework and long runs and possibly partially blocked pipes and requires a UPS2 pump running at its 8M head to feed 21 rads with a theoretical output of 25kw at a 20C dT.
A fairly old Vaillant 438 boiler is being replaced, the boiler is range rated to 24kw so a 25kw replacement boiler should be adequate.
One choice is a 25kw system boiler but because of the very high head required which will still, more than likely be ~ 6M after the system is cleaned, then a LLH or CCts will be required as the max head after passing through the (system) boiler HEX will probely only be ~ 2M at its rated flow rate of 17.92LPM, 1075LPH, also the internal bypass has a maximum setting of 4M, (before the HEX).
The other choice is to install a 25kw heat only boiler and use the existing UPS2 pump and the existing ABV. Question is, assuming a 8M head is still required (even though unlikely) at the rated flow rate, does this cause any problems for the boiler HEX, etc?.
Either it all depends if the hex can take the rated flow and pressure loss (at that flow)
Me personally would go system and ccts with a 1-8 pump externally
There's also UFH (with its own manifold pump) + HW cylinder, would that entail 3 pumps in all, two new, one each for the UFH & the HW cylinder + the existing 8m for the CH?.
Yes if using a system boiler or you could do one modulating pump and one of the ufh etc
Is there a particular way of arranging these flow/return Ts to avoid undesirable mixing?.
  • CCT Sketch.pdf
Do it like a header system and cct the primary if you want I can draw it out etc