I've got a job to replace a Thermostatic Mixer, under a basin in a public premise. When the unit is turned on(service valves) you can hear mains water bypassing to the hot water side, I assume a check valve had broken inside.

Then a though occurred to me do the hw & cw supplies have to be balanced pressure? because the Hw side is fed from a cylinder with a head of about 0.8 bar and the cw is mains.

Thanks
 
Some can work up to 5-1 pressure difference. But best on eaqual pressures.
Non return on the valve can’t be shutting.
 
and also they dont work on gravity pressure (you can Sod faster or it doesnt get hot)
 
Status
Not open for further replies.

Reply to Thermostatic Mixer bypassing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
205
IS IT POSSIBLE TO ADJUST THIS MIXER UNIT? WE HAVE TO HAVE IT TURNED ALMOST FULLY ANTI CLOCKWISE TO GET HOT WATEROUT. THE FRONT PLATE WITH MIRA ON...
Replies
6
Views
268
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
267
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
422
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock