there is a proper way to work out heat loss per room using U values and calculations. Also there is a mears calculator but this is not as accurate. Most engineers jus use their experience to know what size boiler a house requires. but this all depends on if you got double glazing, filled cavity wall or jus a cavity, roof insulation, floor insualtion and air changes.

its easy to calculate the size of the rad for each room but r u asking if a rad can be added without over stretching the boiler?

what is the output of the boiler? what is the outputs of all rads? whats the output of the hot water system? what sizze is the pipe going to the proposed rad? how many rads are off the pipe going to the proposed new rad?

if u can work all that out see if the boiler output is at least 15% greater than the collective outputs of all the other things. then check the pipe is big enough to send enough heat down the pipe to the rads offf that circuit
 
thanks fuzzy, i will work my way through that, and yes I was questioning this so as not too overstretch the boiler capacity. The pipes are 15mm copper, all single panel rads x5 and x4 same downstairs - need to measure though.
Thanks
 
Easy answer:

If normal room (one external wall, one window) 45, warm room (small internal or loads of insulation on external wall) 40 and cold room (two or three external walls, single glazing, large chimney, etc) 50.

Then - size of room multiplied by above number and divide by 1000 gives you the wattage required.

So 4m long x 3m wide x 2.8m tall = 33.6 x 45 / 1000 = 1.512Kw
 