Hi, I was wondering if anyone has any advice please.

i have a towel rail radiator, every few weeks it goes cold at the top and I end up bleeding quite a bit of air from it.

No pressure drop on the system just air! It's been like it for ages but looking for a solution.

Thanks
 
Towel rails do pick up the air out of a system.
That would be understandable if your system is open vented, as the system will constantly absorb and release air as it heats and cools. But if it's a sealed system, as you mention no pressure drop, then air is being absorbed somewhere.
Only exception is is system has been drained and refilled with fresh water for work done, - where air will gather for a few weeks
Auto vents or leaks at valves or boiler could cause air ingress. Or gases from sludge in system, but rare
 
Last edited:
Current and last house both had pressurized combi systems but both did this, bathroom radiator only.

Both cases it did not smell gassy so was not from corrosion of the system. I think I read that air can be taken in on the return side of the pump without a leak showing, not sure if that is correct.

Last house tried changing both lockshield valves on it (radiator) but still filling with air!
It was only when it rusted out (where towels were on it) and we replaced it that it stopped abruptly/completely. So I presumed that air had been getting in at the Bleed valve at the top or oppposite side.

This house move in and large bathroom towel rail taking in air, lots!
Got a heating engineer to replace a suspect lockshield valve on another radiator and reseal the Bleed valve and opposite side of the towel rail. No more air in the towel rail. :)

Whatever you try make sure to reseal the two at the top, it's quick and cheap to do.
 
Status
Not open for further replies.

Reply to Towel radiator constant bleeding of air in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
277
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
439
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
215
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
549
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock