I have a Vaillant Turbomax Plus combi of 2004 vintage. When a cold tap is used nothing happens to the boiler, but as soon as the cold tap is turned off, the boiler starts up for a short time. The hot water demand lights up and the fan (maybe also pump??) runs, but the boiler doesn't get as far as lighting (no burner lit light appears).

Do any of the experts know what causes this, and what the solution is? Thanks for any help.
 
Sounds like you need a shock arrestor fitting on the cold inlet to the boiler

Little test (on the cold tap that fires the boiler up)

Open a cold tap and let it run for a second or two and slowly close the tap does it fire the boiler up
 
You have a dead leg somewhere, most likely where the cylinder used to be.
You can bleed it, if you can find it but the best bet is to remove it
 
Thanks to both of you for your replies. Will try turning the cold tap off slowly when I get home.

Last Plumber>>> There was a cylinder in the cupboard upstairs years ago. Can't see any capped pipes in there, but I suppose it could be under the floor which will be a bit of a mare to get to. If there is possibly a dead leg that I can't find, would Shaun's suggestion of a shock arrestor on the cold inlet solve the problem?
 
Thanks to both of you for your replies. Will try turning the cold tap off slowly when I get home.

Last Plumber>>> There was a cylinder in the cupboard upstairs years ago. Can't see any capped pipes in there, but I suppose it could be under the floor which will be a bit of a mare to get to. If there is possibly a dead leg that I can't find, would Shaun's suggestion of a shock arrestor on the cold inlet solve the problem?

I would guess it's possible if the charge pressure was set lower than the compression you get in the dead leg but that is nigh on impossible to judge, apart from through trial and error. You could try it, you never know !
The dead leg would be on the hot side, probably on the pipe that used to come off the cylinder. I bet it's stop ended under the floor where the cylinder was.
If you do try Shaun's idea, let us know if it worked will you? Like Shaun said, if you do try that, fit it on the cold supply.
 
Status
Not open for further replies.

Reply to Turbomax Starts Up When Cold Tap Turned Off in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
222
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
160
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
376
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
248
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock