Hi
I have installed a UFH system - 2 zones - one area has a screeded floor with standard pipe system in screed, the other is aluminium spreader plates with floor boards over. Wundatrade system.

The whole area has engineered oak flooring over the top. Each zone controlled by hard wired stat and a floor probe set to 27 c.

The problem seems to be that the floor probe quickly reaches temperature and shuts the system down, thus making it hard to reach the required room temperature.

Wundatrade are going to talk me through checking the floor probe temperatures tomorrow, and assuming they're functioning ok I'll ask their advice.

Just wondering if anybody on here has any advice or has experienced this problem. Temp on manifold flow is around 50 c. All worked fine before the flooring went down and we switched to "all sensors".
 
Hi
I have installed a UFH system - 2 zones - one area has a screeded floor with standard pipe system in screed, the other is aluminium spreader plates with floor boards over. Wundatrade system.

The whole area has engineered oak flooring over the top. Each zone controlled by hard wired stat and a floor probe set to 27 c.

The problem seems to be that the floor probe quickly reaches temperature and shuts the system down, thus making it hard to reach the required room temperature.

Wundatrade are going to talk me through checking the floor probe temperatures tomorrow, and assuming they're functioning ok I'll ask their advice.

Just wondering if anybody on here has any advice or has experienced this problem. Temp on manifold flow is around 50 c. All worked fine before the flooring went down and we switched to "all sensors".
Why have you used floor probes? I'd be inclined to go air sensor as the wood floor will give massive thermal resistance and heat up quite hot before the heat gets through, thus satisfying the stat. I've done one recently with engineered flooring and after a great deal of faffing about and the custard whining at me being cold, the tmv had to be about 50 degrees to get the heat to come through the floor. I installed the loops before screeding and came to start 2nd fix and was alarmed to see 20mm engineered flooring WITH underlay, although they said tiles were going down.

Ffs!!!!

Energy efficiency went straight outta the window!
 
Hi
I have installed a UFH system - 2 zones - one area has a screeded floor with standard pipe system in screed, the other is aluminium spreader plates with floor boards over. Wundatrade system.

The whole area has engineered oak flooring over the top. Each zone controlled by hard wired stat and a floor probe set to 27 c.

The problem seems to be that the floor probe quickly reaches temperature and shuts the system down, thus making it hard to reach the required room temperature.

Wundatrade are going to talk me through checking the floor probe temperatures tomorrow, and assuming they're functioning ok I'll ask their advice.

Just wondering if anybody on here has any advice or has experienced this problem. Temp on manifold flow is around 50 c. All worked fine before the flooring went down and we switched to "all sensors".
Why have you used floor probes? I'd be inclined to go air sensor as the wood floor will give massive thermal resistance and heat up quite hot before the heat gets through, thus satisfying the stat. I've done one recently with engineered flooring and after a great deal of faffing about and the custard whining at me being cold, the tmv had to be about 50 degrees to get the heat to come through the floor. I installed the loops before screeding and came to start 2nd fix and was alarmed to see 20mm engineered flooring WITH underlay, although they said tiles were going down.

Ffs!!!!

Energy efficiency went straight outta the window!
 
Why have you used floor probes? I'd be inclined to go air sensor as the wood floor will give massive thermal resistance and heat up quite hot before the heat gets through, thus satisfying the stat. I've done one recently with engineered flooring and after a great deal of faffing about and the custard whining at me being cold, the tmv had to be about 50 degrees to get the heat to come through the floor. I installed the loops before screeding and came to start 2nd fix and was alarmed to see 20mm engineered flooring WITH underlay, although they said tiles were going down.

Ffs!!!!

Energy efficiency went straight outta the window!

The flooring manufacturers probably wont guarantee the floor if its over 27 degrees. They are worried the floor will expand and lift.
 
The flooring manufacturers probably wont guarantee the floor if its over 27 degrees. They are worried the floor will expand and lift.

Its been fine so far for two months, luckily there's a good expansion joint around the room.

They know they've done wrong for not keeping me in the loop regard flooring choice. No heat would come through that made a difference at 30degrees.

Nay mind, that's what happens when you act clever.
 
So as kozak says its a requirement from the flooring co. and stated in the Wundatrade instructions to fit floor probes.
I agree the heat just gets trapped under the floor and shuts it down, but short of ignoring all the recommendations what can i do?
 
So as kozak says its a requirement from the flooring co. and stated in the Wundatrade instructions to fit floor probes.
I agree the heat just gets trapped under the floor and shuts it down, but short of ignoring all the recommendations what can i do?

He responded to my post, your answer is to convert to air sensor.
 
It maybe as simple as going into the thermostat settings and setting air temp setting instead of floor probe setting
 
I can do that but if there's a problem with the flooring I dont have a leg to stand on.
You'll have to go through the rigmarole that I've just been through. I turned the tmv up 5 degrees everyday until they informed me they were starting to feel warm enough.
 
Status
Not open for further replies.

Reply to UFH & Engineered Oak Flooring in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock