My underfloor heating is set at 21 on the stat but the floor area feels cold to touch. I was expecting to feel a little warmth from it. I have since discovered that my builder has laid a 30sqm pack over a 50sqm area. Is this as bad as it sounds? Thanks in advance
 
Unfortunately - Yes.
Were there any heatload calculations done?

Do you have any photos of the piping at the time of installation?
 
Sounds like an expensive error you can either get it redone or pursue "builder" to try and get some money off. Begs the question why they didn't use an experienced plumber. See so many poorly installed ufhs by builders who think it's just a case of throwing it in
 
There's no such thing as a 30m2 pack... As ... It all depends upon the heat loss of the room, the designed flow temperature, and possibly the heat source.

Ask him for the heat loss calculations.

Old leaky buildings like the one I surveyed today, 150W/m2 house size 80m2 heat load 12kW
Then there's the new build we're working on 450m2 , 26W/m2 Heat load 12kW

The design and installations are completely different... (the first isn't suitable for ufh, the second we have to cool the house in the summer...)

What length of pipe did he install, how many loops, serpentine or snail,

What was the designed flow temperature for the underfloor heating?
Has he connected the flow and return the wrong way round?
Is the TMV on the manifold configured correctly?
Does the underfloor heating have it's own circulation pump?
Did he just tap off the existing heating circuits?
Are there in screed stats or just air stats?
 
Its a pity there arent more like worcester out there, too many doing things they dont understand! ps I dont touch ufh, as I know fa bout it :)
 
Status
Not open for further replies.

Reply to Wet underfloor heating system in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, I wanted to ask a general question about an underfloor heating system our plumber is proposing and if this solution will be sufficient...
Replies
1
Views
503
I'm attending a wet underfloor heating system, it's an old one ..No flow meters, just adjustable valves on the returns with conventional...
Replies
3
Views
549
Evening all, I’m currently in the process of refurbing my house, and have opted to wet UFH for the whole of the downstairs. The upstairs will be...
Replies
7
Views
644
I have a OMNIE designed wet underfloor heating system on three floors. Ground and 2nd floors work well with those two floors having a single...
Replies
6
Views
917
Got an underfloor heating to install and Ive done a few repairs on manifolds etc but this is the first design and install for me. Advice and tip...
Replies
13
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock