I put some x400 into my old system to try and cure a kettling issue. after a few days it seems better but the system doesn't seem to heat up as well. ideas.
 
The heat exchanger is probably cleaner so therefore the flow of water through the boiler will be greater so it will give the water less time to heat up.

Check what pump speed is on/ size of pump
 
probably just over thinking/ checking. turn your stats up if your cold :)
 
watching temps on a digital k-type meter and the flow and return differential has dropped from 11-12 to 6-8, and the flow temp is struggling to reach into the 50's.

obviously the x400 has shifted something, but not sure I that's a good thing or not.
 
ok temps before x400 with pump on setting 2 and boiler stat on 6 (max):

5min 34 diff 9
10min 38 diff 9-10
15min 43 diff 10
20min 46 diff 10
25min 50 diff 11
30min 53 diff 12
35min 57 diff 13
40min 62 diff 14
45min 67 diff 16
50min 71 diff 17-18

maybe trv's were closing, but I still have a rad in the hall that's dosent have a trv and both lockshields are fully open.

after x400 for about 5 days:

0min 23 diff 6-7
5min 28 diff 8
10min 31 diff 8
15min 35 diff 8
20min 38 diff 8
25min 41 diff 8
30min 44 diff 9
35min 47 diff 9
40min 50 diff 9-10

52min 58 diff 11

then about 30mins later with boiler cycling on its stat:

65 diff 10

so it appears to have made the differential more stable, but at the cost of a very long heat up.
 
New boiler new boiler. It's been through the wars and as its in a low spot probably full of sludge. Blast it out with mains pressure and a wet vac. Use the capped grav circs
 
the system is, I think, too large for this boiler.

28mm runs 10m to unvented and pump from there to rads.

some rads are more or less off due to truning down the trv's, but this is the list:

3 doubles
9 singles

probably only 8 of those are actually set to give off heat, and 3 of those are set to very low output.
 
also bought a magnaclean 2, which I plan to fit this weekend, hopefully this will help trap any crud the x400 has put into circulation.
 
Last edited:
Probably fine without megaflow. But megaflow will eat all that heat during heat up
 
Status
Not open for further replies.

Reply to x400 indirectley causing system to run cooler? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock