Hi

about an hour ago all the lights in my house tripped out. I went to the fuseboard and one switch was down. Flicked it back and it tripped out immediately.

few moments later theres and acrid smell and a little smoke in the room

tracked the smell down to the boiler, took the cover off and was met with this (see photo)😳

have got someone coming out tonight to look at it. In the meantime have turned the power off.

Any idea what would cause this earth wire to melt?

It’s a Worcester Bosch junior 28, has been in about 8 years without any problems
 

Attachments

  • 341A9C9E-8DEE-4539-A38A-050F0D218436.jpeg
    341A9C9E-8DEE-4539-A38A-050F0D218436.jpeg
    108.6 KB · Views: 102
Have a degree in electrical engineering and do frequent the other forum, lol
I tend to only look at ops that are either pure gas or electrical, my best friend is plumber 😛
I have a friend who is an Electrician we have had him with us for years...we drink with him
...his name is 'Mad Ian' ..he is quite often 'short on his round' usually never buying me a beer before he slopes off ...but we like and most importantly trust him.......centralheatking
 
Man has been to check the boiler and seems to think it's an electrical fault somewhere on that circuit. the wiring in the fuse box next to the boiler looks a bit dodgy, live and neutral wires both have cuts in them and the earth wire sleeve has melted there too

Electrician coming tomorrow.

Thanks for all the advice on here
 
I imagine the ground fault is somewhere inside the boiler somewhere. Lots of places and components where this can happen. I hope this sudden rush of current hasn't damaged any more parts. Might be advisable to have both electrician and engineer there at same time
 
We’re back in business!

Looks like it was a plug socket in the kitchen (same circuit as boiler) that was at fault. As the electrician took each socket on the circuit out one by one, this one was all burnt out inside. The live wire had melted onto the earth cable. He says the live wire wasn’t secured in the terminal properly and had just come loose over time.

presumably this had made the earth wire ‘live’?

I’ve no idea why it then went into the cellar and nearly set the boiler on fire, when everything else is fine?


Anyway a couple of new sockets later, plus new fuse and socket fitted to boiler supply and all seems well.
 
  • Like
Reactions: DuncanM
We’re back in business!

Looks like it was a plug socket in the kitchen (same circuit as boiler) that was at fault. As the electrician took each socket on the circuit out one by one, this one was all burnt out inside. The live wire had melted onto the earth cable. He says the live wire wasn’t secured in the terminal properly and had just come loose over time.

presumably this had made the earth wire ‘live’?

I’ve no idea why it then went into the cellar and nearly set the boiler on fire, when everything else is fine?


Anyway a couple of new sockets later, plus new fuse and socket fitted to boiler supply and all seems well.

If the live was loose then it like he said over time it will work its way out of connector. You are right to a degree, the live wire when comes in contact with the earth creates a circuit back to source, without a resistive load you have a sudden, massive rush of current, this rush of current (over current) generates heat and melts any fuse or trips any MCB, which is what they're supposed to do, protect the system and prevent fires.
 
  • Winner
Reactions: redd
Great news. Earthing within a house can have many parallel paths. The boiler and associated pipework can be a good hub for many parallel paths. The good news is that the breaker did its job and saved more serious damage to the property. Hopefully the electrician has checked all associated devices that were on that cct as its certainly stressed ALL earth routes back to the consumer unit.
 
  • Agree
Reactions: SJB060685
If the live was loose then it like he said over time it will work its way out of connector. You are right to a degree, the live wire when comes in contact with the earth creates a circuit back to source, without a resistive load you have a sudden, massive rush of current, this rush of current (over current) generates heat and melts any fuse or trips any MCB, which is what they're supposed to do, protect the system and prevent fires.

yeah, pretty lucky I suppose!

Going to get them back to fit a new consumer unit and rewire that circuit shortly, as it looks like it’s been in since about 1970

thanks everyone on here for the advice 🙂
 
  • Like
Reactions: SJB060685
We’re back in business!

Looks like it was a plug socket in the kitchen (same circuit as boiler) that was at fault. As the electrician took each socket on the circuit out one by one, this one was all burnt out inside. The live wire had melted onto the earth cable. He says the live wire wasn’t secured in the terminal properly and had just come loose over time.

presumably this had made the earth wire ‘live’?

I’ve no idea why it then went into the cellar and nearly set the boiler on fire, when everything else is fine?


Anyway a couple of new sockets later, plus new fuse and socket fitted to boiler supply and all seems well.

Whilst that may have been identified, this doesn't explain why the "short" didn't use the circuit CPC (earth) back to the fuseboard .......... which is what I would have expected unless the circuit cpc wasn't connected at the fuseboard.

Was this circuit a Ring or Radial and was it tested properly for continuity?
 
Whilst that may have been identified, this doesn't explain why the "short" didn't use the circuit CPC (earth) back to the fuseboard . which is what I would have expected unless the circuit cpc wasn't connected at the fuseboard.

Was this circuit a Ring or Radial and was it tested properly for continuity?

Hi Murdoch.

I'm always keen to further my knowledge about electricity. Can you explain to me why this ground fault may have taken this path rather than back to fuse board?
 
Hi Murdoch.

I'm always keen to further my knowledge about electricity. Can you explain to me why this ground fault may have taken this path rather than back to fuse board?

Maybe my poor response but the reason for ALL 240v cables in a domestic setting to have a CPC (earth) which is continuous from the fuseboard to the end of the circuit is so that this earth is the path such a fault would take. This includes lighting circuits

If under fault conditions, the fault took "another" path back to the fuseboard, this would suggest that the circuit with the fault did not have a CPC (earth) back to the fuseboard.

In the fault as described, the lack of earth would explain the unusual "path", which took another route back to the fuseboard.

On a slightly different subject, boiler wiring, for mains powered room stats don't always show the CPC, but it must be connected to the boiler ......... or else in the event of a fault, the current will find another path - which could well be you!
 
  • Informative
Reactions: SJB060685
Whilst that may have been identified, this doesn't explain why the "short" didn't use the circuit CPC (earth) back to the fuseboard . which is what I would have expected unless the circuit cpc wasn't connected at the fuseboard.

Was this circuit a Ring or Radial and was it tested properly for continuity?

the electrician did say that the electrics in the property weren't earthed, and were relying on an earth on the gas and water pipes?

He advised me to call my supplier (E-On) and get them to sort this earth out. After half an hour on the phone to Bangalore or somewhere, Ive got someone coming tomorrow to fit a smart meter ffs. 🤣 Despite telling the chap countless times I need someone to look into the incoming connection, he insists its something they'll deal with as part of the smart meter install. The cynic in me suspects he's taking cr@p and is on commission for getting someone out to install a smart meter

Would this usually be the job of the DNO (northern powergrid in this case), or something I should get my own electrician to sort?
 
the electrician did say that the electrics in the property weren't earthed, and were relying on an earth on the gas and water pipes?

He advised me to call my supplier (E-On) and get them to sort this earth out. After half an hour on the phone to Bangalore or somewhere, Ive got someone coming tomorrow to fit a smart meter ffs. 🤣 Despite telling the chap countless times I need someone to look into the incoming connection, he insists its something they'll deal with as part of the smart meter install. The cynic in me suspects he's taking cr@p and is on commission for getting someone out to install a smart meter

Would this usually be the job of the DNO (northern powergrid in this case), or something I should get my own electrician to sort?


Sounds like you need a new electrician ...

Did said electrician give you any paperwork for your work ?
 
Sounds like you need a new electrician .

Did said electrician give you any paperwork for your work ?

no paperwork yet, other than a bill 😱

What makes you say that anyway? I’m guessing you’re suggesting the electrician should be the man to sort out this earth issue rather than my supplier or DNO?
 
no paperwork yet, other than a bill 😱

What makes you say that anyway? I’m guessing you’re suggesting the electrician should be the man to sort out this earth issue rather than my supplier or DNO?

No decent competent spark would leave you in this situation without some form of written note for the client to understand

There are homes around without an earth, there are home around that use gas or water pipes for the earth .... only a private metal water supply pipe can be considered suitable for use as an earth ....

Where does the electrical supply enter your home? Overhead or under ground?

Not enough information to comment further tbh and I would recommend you get a 2nd opinion ...

Maybe the op could post some pictures
 
  • Informative
Reactions: SJB060685
The electrician says it has an earth, but it’s not sufficient and it’s not with the electrical supply? It’s on the gas and water pipes?

The house has a normal underground supply, all the utilities are in the cellar

Here’s a pic of the fuseboard setup and the earthing around the boiler gas and water pipes...
 

Attachments

  • 476E15E7-D2AE-44DF-8AF0-23431C2B26AC.jpeg
    476E15E7-D2AE-44DF-8AF0-23431C2B26AC.jpeg
    125.3 KB · Views: 40
  • DE0D53AE-BB56-47B3-B3BD-F249ABDBCDF7.jpeg
    DE0D53AE-BB56-47B3-B3BD-F249ABDBCDF7.jpeg
    143.3 KB · Views: 45

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.