Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Honeywell motorised valve not working correctly?

View the thread, titled "Honeywell motorised valve not working correctly?" which is posted in Central Heating Forum on UK Plumbers Forums.

I have a Honeywell value (V4073A1039) which doesn't seem to be operating correctly, basically not opening when using heating and not closing when using water. The issues is shown in this video.....
 
Is it new? Has it always been like that? Seems like it might be motor failure or wired wrong.
No it's not new. Not sure if it's always been like that only been in the house since December but just got around to looking at it now as I was sure it wasn't acting correctly.

Can it actually be wired up incorrectly??, As I haven't look properly but I was under the understanding that there's only 5 wire's, earth, neutral, live and then the 2 signal wire's???. But I thought it doesn't matter which way the signal wire's go???

Also even when I turn the water or heating off the motor is still active and keeping the valve open as I need to turn the power off to the control panel and once I do that I hear the motor realising the valve, so it seems that the control panel is still sending a signal to the motor to keep the valve open even when I turn the heating and water off
 
The valve is not operational when only hot water is required. The boiler is turned on by the HW cylinder thermostat.

If only CH was the last call, the valve will remain in the CH only position. This is "feature" of the V4073A valve. The valve only uses 6 Watt, which is insignificant, though it will get warm. Calling for HW or turning the power off will reset the valve to the default HW only position.

The diagrams below show the various states of the valve

(Better pics in my next post)
 

Attachments

  • Mid pos -1.jpg
    Mid pos -1.jpg
    12.4 KB · Views: 46
  • Mid pos -2.jpg
    Mid pos -2.jpg
    50.1 KB · Views: 47
Last edited:
The valve is not operational when only hot water is required. The boiler is turned on by the HW cylinder thermostat.

If only CH was the last call, the valve will remain in the CH only position. This is "feature" of the V4073A valve. The valve only uses 6 Watt, which is insignificant, though it will get warm. Calling for HW or turning the power off will reset the valve to the default HW only position.

The diagrams below show the various states of the valve

Oh, so it appears its all working correctly then?

So if i ask for CH its normal for the motor not to move at all, as the default position of the valve is for the CH and so doesn't need to send power to the motor to move the valve as its already in the default open position for CH?

But why if i ask for HW the motor activates but when i turn the HW off the motor doesn't move the valve back to the default position which is for CH?, surely the motor should activate (be it to open or close the valve) again once i turn the HW off??
 
Last edited:
Oh, so it appears its all working correctly then?

So if i ask for CH its normal for the motor not to move at all, as the default position of the valve is for the CH and so doesn't need to send power to the motor to move the valve as its already in the default open position for CH?

But why if i ask for HW the motor activates but when i turn the HW off the motor doesn't move the valve back to the default position which is for CH?, surely the motor should activate (be it to open or close the valve) again once i turn the HW off??
The default position, when there is no voltage to any valve wire is for port B to be open. This is the connection to the HW cylinder. Port A is the CH connection.

If CH was the last call, the valve is held in the CH only position. So there is no need for the valve to move if there is a subsequent call for CH.

If the valve is held in CH only and you now call for HW, the motor does nothing. Turning HW on removes voltage from the grey wire, so the valve can return to the default HW only position under the power of the spring.

Look carefully at the second set of diagrams I posted and all will be clear.
 
From the FAQ sheet: https://heatingcontrols.honeywellhome.com/documents/All/pdf/975.pdf

"When this Heating demand is satisfied, during a Heating ON period, 50V to 150V (voltage can vary according to the supply) will remain on the orange wire and the valve will continue to be energised and warm to the touch. Switching Hot Water ON or turning OFF at the mains will de-energise the valve and it will spring return back to the Hot Water only position until the next demand"

The default position is port B to be open (HW only). Which means if there's no power to the valve, that's where the spring will have it rest.

Where you are getting confused is at 1 min 5 in your video. When you turn the HW off, you are expecting the valve to move - it will not. At this point, the valve has 240V on the grey wire (from the HW off terminal of the programmer) - so from the quoted text above, the valve will maintain it's current position (which happens to be port B open / HW only). You then proceed to move the valve manually, which means you've now moved it to CH only (port A open / CH only), and the valve maintains that position because it has power on grey.

At 1 min 26, you turn the heating on, expecting the valve to move, but it is already in the correct position.
 
I always find it difficult to understand how it stays in mid position when the HW & CH are switched off, I thought it might motor to CH only as there is now no power on the white wire (only), probably misinterpreting what last port of call really means.
 
It never stays in mid position after a call. If HW was last call then its returned to HW. If CH was last port of call its held in CH position. Theres a resistor and diode involved. I will upload an image, although its been shared before.
 
I have no problem in understanding the last port of call if it has been in either CH only or HW only, on CH only the valve is (240V) kept energised by the grey wire via SW1 only (HW off) to keep it it in this position, on HW only the valve is in its unpowered state anyway so remains there.

If its in mid position, it is kept there by feeding 240V via the white wire through a diode and a resistor which reduces it to ~ 60/70 DC volts, SW1 is now also closed to the grey wire but no problem as no voltage from this wire. If you then switch off the CH first then the valve will return to its unpowered state which is HW, if you then switch off the HW there will be 240V on the grey wire but because SW1 is now opened from the grey wire then the valve will stay unpowered. But if you switch the HW off first then you will have 240V on the grey wire which will power the valve to CH only and it will remain there if you then switch off the CH, is this how it might work?.
 
Yes mate. That's not the best image but one I quickly found for you. Try these two.
If in mid position and you swith CH off. You will lose power to the white wire, which is what's holding the valve in mid position with pulses of DC. The valve will spring return to HW and close switch 1. If you turn off HW first then grey wire will supply 230 volts and fully motor over to CH position and switch switch 2 over supplying 230 volts to orange.
Whatever is the last port of call is held in either case. One of the problems with this design though is if CH was the last port of call the valve remains energised and motored over to CH, which is why they frequently burn out.
 

Attachments

  • IMG_1518.PNG
    IMG_1518.PNG
    2.3 MB · Views: 43
  • IMG_1519.PNG
    IMG_1519.PNG
    2.2 MB · Views: 47
Thanks, that's what I thought might happen alright, so obviously cannot stay in mid position except calls for both HW&CH, still, a very ingenious design, it also has another resistor to give a AC de magnetizing current.
 
H/w is default position. If Last call was central heating valve stays until next call depending on cylinder stat satisfied and its hot water priority..
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Honeywell motorised valve not working correctly?" which is posted in Central Heating Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
BlockABoots,
Last reply from
spanner,
Replies
22
Views
9,398
Back
Top