Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Firebird oil boiler hot water

View the thread, titled "Firebird oil boiler hot water" which is posted in Boiler Advice Forum on UK Plumbers Forums.

My firebird oil boiler hw supply is luke warm, but does heat up slightly when run if the ch is on at the same time.
Is this a faulty diverter valve?
If so could I replace this myself as I've heard they're expensive to fix.
Tia
 

Attachments

  • 20230428_172401.jpg
    20230428_172401.jpg
    316.4 KB · Views: 63
The heat store should still get very hot even if blender valve is faulty. Can you switch off the boiler, run off say 20 or 30 liters of HW, shut the HW tap then fire up the boiler and see how long it runs for.
 
The 35kw boiler must have sent 5.53 kwh somewhere, assuming.iit's to the store then that's sufficient to raise 125L from 25C to 65C . Are you sure the store isn't very hot? The only other route for that 5.53kwh is to the CH?
 
Are the boiler CH flow and return pipes hot for this 10 minutes, I can't imagine the heat going anywhere else, any idea, even roughl of the heat store volume?.
 
Can't find a schematic of a Firebird Combi but its probably something like this Grant where the stored water is primary water, might be worth checking the non return valves and that the heating pump isn't running when HW requested. The Grant primary store is 32.5 Litres, total contents 53.5 litres.

1683899566667.png
 
Last edited:
Two pumps = no diverter.

Need to know if rads are getting hot when hot waters ran. If so it's a non return valve.
 
They claim 120L available at 20LPM at a 40C dT from the 40L primary store (78C) presumably as the boiler will be firing at 35kw output as well.
Any idea of the continuous flowrate at say 40C once the store has fallen to say 50C?, there will obviously be a dT between the PHE and the DHW temperature, is say 16.0/16.5LPM at 40C achievable at a mains/DHW dT of 30C.
 
Last edited:

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Firebird oil boiler hot water" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Westernr1,
Last reply from
John.g,
Replies
27
Views
3,052
Back
Top