Hi My gas cooker has been disconnected because of a half MB drop in gas pressure. The gas test was carried out by a CORGI registered engineer. The landlord instructed him to disconnect my cooker because that is the source of the half a MB leak. I refused permission. The landlord contacted National Grid who disconnected my cooker.

I understand that a 4 MB drop in gas pressure is permissible. Half a MB is a very slight variation in gas pressure and think the landlord has over-reacted. Does anybody know if legally I can insist the landlord arranges to have my cooker re-connected?
 
half a mbar drop is permisible, was this gas leak on the pipework or the appliance itself?? not sure about the legality from a landlords point of view but to be fair a gas leak is a gas leak.

also why was the engineer not instructed to carry out a repair instead of just dissconecting the appliance??
 
Last edited by a moderator:
The half a MB gas leak is from the cooker, not the gas pipes supplying the cooker. From what I have heard, gas engineers would not normally disconnect a cooker because of a half MB drop in gas pressure. This has happened because the landlord has insisted upon it. I wonder if legally I can ask for the cooker to be re-connected?
 
The half a MB gas leak is from the cooker, not the gas pipes supplying the cooker. From what I have heard, gas engineers would not normally disconnect a cooker because of a half MB drop in gas pressure. This has happened because the landlord has insisted upon it. I wonder if legally I can ask for the cooker to be re-connected?


the crux of the matter is how the 0.5mb leak was found, IF it was because there was a smell of gas reported at the appliance then it is right that it is disconnected, if the 0.5mb leak was found on a routine test for say the annual safety check AND the cooker is an existing appliance then it DID NOT NEED TO BE CAPPED, as you are allowed either 4mb or 8mb depending on the meter, with no smell or report of smell of gas etc, so give a wee bit more info on the background to the finding of the leak and i can confirm
the other side of the coin is that landlords get a pretty hard time for not complying with the regs and endangering tenants, this landlord seems to be over cautious to the extreme, however he may argue it is good practice to have no leak in his property, and who could argue against his safety stance,
 
Last edited by a moderator:
You can understand the landlords point of few although he has to fix it or get you a new cooker. Just ask him what his plan is if your paying rent he should sort it out quite quickly
 
If it was hes cooker i would suspect he would of left it. I could be wrong and he might just want everything spot on, but knowing landlords i doubt it. I wouldnt of thought transco would of been able to cap it if it was within tolerance and no smell of gas?
 
Last edited:
99.9% chance it is tenants cooker and NOT landlords or it would have been left as it is perfectly acceptable, how do you find a 0.5mb leak if there is no smell
 
Hi My gas cooker has been disconnected because of a half MB drop in gas pressure.

I think the point is that it was the OPs cooker not the landlords. If it was? then in my opinion the landlord was well within his rights to disconnect it.

If permission to disconnect is refused and the Transporter is called out they won't care if there is a smell or not. If it is a reported leak they will test it then either make sure the appliance is disconnected, cap the meter or if that is still refused chop the supply. Reconnection is then at the expense of the tenant.
 
If permission to disconnect is refused and the Transporter is called out they won't care if there is a smell or not. If it is a reported leak they will test it then either make sure the appliance is disconnected, cap the meter or if that is still refused chop the supply. Reconnection is then at the expense of the tenant.[/QUOTE]

I thought they only came out if it exceeded its tolerance or reported smell and permission to cap refused. Cheers
 
If it is reported as an escape the TSE just picks up the job as it is written or phoned to him. If it is for refusal to disconnect it's the same.
His job is to make sure it is made safe regardless and he won't negotiate on whether there is a smell of gas or not.
Test, acknowledge there is a drop and make safe. No arguments.
 
Think we are missing the point here

You can test the existing installation with existing appliances fitted and are allowed a drop depending on pipe and meter size, this is a all combined drop, which is why you have different drop allowances

The test was carried out a drop was found, fill in paperwork and away you go

However, there have been further investigations, the drop has been isolated with cooker, pipework and other appliances most have been tested separately to show this

Therefore cooker should not have been reconnected however it was, there is no rule that says a appliance by it self can have any pressure drop therefore we have a appliance connected to the supply that should not be, thus supplier quite within their rights to cut off

So in answer to op, no you have no legal recourse and your attitude is questionable at best

imho
 
Last edited by a moderator:
That is about it.

The 4mb allowable drop (if no smell) is with appliances connected and assumes there may be a small drop on the appliance(s).

If you decide to isolate the appliances (you don't have to although it would be good practice) you are then testing pipework which has no allowable drop therefore any faulty appliances need to be rectified or capped off.

Say you were fitting a hob to an existing supply already feeding a boiler and a fire. Test before carrying out the work and find a 2mb drop. This is acceptable if there is no reported smell of gas so you note the drop, fit the hob and retest. As long as the drop is no more than it was on the first test it is fine. Just inform the customer that there is a drop that is within limits and leave the decision to him/her.
That is why you should get a testing and purging pad, note the results and leave a copy with the customer.

If however, when finding the drop on the first test you decide to isolate the appliances and these are found to be at fault, they MUST be capped or repaired before you continue.
If you find there is still a drop with appliances isolated (pipework) you cannot fit the hob unless you (or someone else) trace the leak.
This may lead to a pi..ed off (but safe) customer (see above lol) who may then have no heating or gas.

At the end of the day it is your decision.
 
Last edited by a moderator:
That is about it.
The 4mb allowable drop (if no smell) is with appliances connected and assumes there may be a small drop on the appliance(s).

tam i have deleted rest of your post as i agree with it, but the bit above confuses me, i agree with what you have written, but surely the fact that it is traced to the appliance, with no smell of or report of smell of gas, then this is the exact situation of microscopic leak(s) that is allowed under the 4/8mb rule and can be left connected, there is no statement that the up to 4mb leak has to be spread over several appliances, merely that there is existing appliance(s) connected rather than new?
 
Should have written 4mb drop with any existing appliance as you say.