Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Honeywell Evohome with 2 zone heating

View the thread, titled "Honeywell Evohome with 2 zone heating" which is posted in UK Plumbers Forums on UK Plumbers Forums.

Is there any advice on using Honeywell Evohome with 2 zone heating. Honeywell support are pretty useless and give conflicting advice. They suggested I ask my installer (but my installer suggested I ask Honeywell). I found a support article on the Honeywell Resideo website by Googling "How-to-control-more-than-one-heating-zone-valve-with-evohom". This seems to suggest binding the two port valves (which is not what I want to do).

Ideally I would have HR91 Radiator Controllers on some but not all rads. This doesn't seem like it is supported. I'm not even clear if I can have HR91 Radiator Controllers on all rads in one zone but not the other.

If Honeywell Evohome does not support dual heating zone systems well then does any other system?

It seems worrying that Honeywell don't seem to have a clue how to support this given the fact that Building Regulations Part L 2010 mandate two zones. Even if Evohome makes two zones redundant, it does not seem sensible to tell people just to bind the zones.
 
I don’t know this for sure but I suspect that you’ll need to make sure both zone valves are always open.

each trv will call independently for heat so the heating needs to be able to flow to anywhere (if that makes sense)
 
It was a simple question of what you were trying to achieve - as you didn’t explain fully in your original post!
I’d like to control one zone of my house using room based Trvs and the other using a zone thermostat. Even if I ultimately decide to instal smart trvs everywhere , I want the system to use the zones to send heat to the zone that is calling for heat .
 
I’d like to control one zone of my house using room based Trvs and the other using a zone thermostat. Even if I ultimately decide to instal smart trvs everywhere , I want the system to use the zones to send heat to the zone that is calling for heat .
Yeah you can do that.

Zone 1 with TRVS - remove or lock open the Motorised valve. Disconnect electronically.

Zone 2 - set up as an extra zone controlled by Zone Valve with an additional stat or just the panel as the stat.
 
Yeah you can do that.

Zone 1 with TRVS - remove or lock open the Motorised valve. Disconnect electronically.

Zone 2 - set up as an extra zone controlled by Zone Valve with an additional stat or just the panel as the stat.

I think I'll get a Drayton Wiser. They have a system that is designed to work with two heating zones (using the motorised valves).
 
No matter what system you use - you're going to struggle having some rads with eTRVs and not (In different zones). Whenever there is a demand on a TRV on a rad, any rads within that zone that don't have eTRVs on will heat. The zone valves don't make the slightest bit of difference tbh.

You'd need to do one zone fully with eTRVs or not. Drayton won't be any different.
 
No matter what system you use - you're going to struggle having some rads with eTRVs and not (In different zones). Whenever there is a demand on a TRV on a rad, any rads within that zone that don't have eTRVs on will heat. The zone valves don't make the slightest bit of difference tbh.

You'd need to do one zone fully with eTRVs or not. Drayton won't be any different.
I plan to have eTRVs in one zone but I still think that zone should use the 2 port valve. I think this is how the Wiser works
 
The trvs are battery powered and communicate with radio. Doesn’t seem sensible to rely on these over a hard wired mains powered 2 port valve
The eTRVs would have to open before the zone valve would trigger anyway? The zone valve is only triggering the boiler - if anything it's an extra thing to go wrong. Why are you bothering if you're that concerned - just leave it as two zones with a smart controller and not bother with the eTRVs
 
Yeah you can do that.

Zone 1 with TRVS - remove or lock open the Motorised valve. Disconnect electronically.

Zone 2 - set up as an extra zone controlled by Zone Valve with an additional stat or just the panel as the stat.
Hi! I want to to the same, one room with radiator and the other with controller sensor as main temperature sensor. I try to setup in different ways, but every day, at 22:33 minutes I got the error: "Comms Fault". Should i set up the evohome controller as Zone valve and I need something else extra for that? Thank you!
 
Hi! I want to to the same, one room with radiator and the other with controller sensor as main temperature sensor. I try to setup in different ways, but every day, at 22:33 minutes I got the error: "Comms Fault". Should i set up the evohome controller as Zone valve and I need something else extra for that? Thank you!

Those evoHome 'comms fault' can be a real pain.

Are you sure it is not just the one fault from days ago - you need to clear the error log in the controller and see if it happens again or not.
It's suspicious that it is exactly the same time...... so this is quite possibly the issue: just 1 one comms blip.

We run a 2 Zone system here on UFH in two big church hall rooms. And after 2 years started getting the 'comms faults' - but sporadically.

If it genuinely is happening fresh each day - gIven that it is always at the same time - is it possible it is electrical interference - have you (or your neighbors) something motorised that fires off at 22:33? New Heatpump in the street?

How long has your system been in and running?
 
Last edited:
Is there any advice on using Honeywell Evohome with 2 zone heating. Honeywell support are pretty useless and give conflicting advice. They suggested I ask my installer (but my installer suggested I ask Honeywell). I found a support article on the Honeywell Resideo website by Googling "How-to-control-more-than-one-heating-zone-valve-with-evohom". This seems to suggest binding the two port valves (which is not what I want to do).

Ideally I would have HR91 Radiator Controllers on some but not all rads. This doesn't seem like it is supported. I'm not even clear if I can have HR91 Radiator Controllers on all rads in one zone but not the other.

If Honeywell Evohome does not support dual heating zone systems well then does any other system?

It seems worrying that Honeywell don't seem to have a clue how to support this given the fact that Building Regulations Part L 2010 mandate two zones. Even if Evohome makes two zones redundant, it does not seem sensible to tell people just to bind the zones.
I have a 3 bedroom semi detached house with 11 radiators. Each radiator is a zone so every area is individually controlled. This seems over-kill, but it works very well. The ground floor is open plan, all radiators are set to the same temperature. The radiator(s) on the north side of the house come on more often so the temperature is more even.
I am not sure if this helps!
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Honeywell Evohome with 2 zone heating" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
samwardill,
Last reply from
Boateye,
Replies
17
Views
2,787
Back
Top