In short, can anyone tell me what max load of a U6 meter is, is it 65KW or 6m3/hr.
I am looking at two boilers at 30kw and 24kw, plus one gas cook at 9kw, total usage is 63KW/hr which is within the 65KW.
However, if I look at the gas flow rate, 30kw boiler at 3.4m3/hr and 24 KW at 2.59m3/hr. Just two boilers already reach 6m3/hr. Does that mean I need to have a U16 meter in order to have a gas cook.
Many thanks,
 
U6 has a maximum throughput of 6m3/hr
 
U6 has a maximum throughput of 6m3/hr

Many thanks, BLOD.
However, I understand that the way to convert KW to hours gas rate is to multiply 0.094. So for 6m3/hr equivlant to 64KW. If I didn't ring up the boiler manufacturer to ask for their gas hourly flow rate, I could just calculate two boiler 30kw+24Kw=54KW x 0.094=5 m3/hr plus 9Kw cookx 0.094=0.84m3/hr. The total would be within 6m3/hr.

If you are to issue a Gas Safe Certificate for a landlord, what would you do, do you just calculate the load or check the individual boiler manual?
 
you need to take diversity of use into account as well, below is an extract form BS 6400-1 which tells you how to calculate the actual load

Annex A (normative)
Sizing of meters

A.1
Diversity factor

A diversity factor is given to each type of appliance according to the

normal degree of intermittence of use. Where there is only one or two

appliances (e.g. combination boiler and cooker) the diversity factor

shall have a value of one. Where there are more than two appliances the

diversity factors listed in Table A.1 shall be used.

A.2
Meter size calculation

To calculate the size of meter required, multiply the maximum heat

input of each appliance by its diversity factor, add these figures, convert

to megajoules, and divide the total by the calorific value of the gas

(typically 39 MJ/m
3 for 2nd family gas). The following is an example of

such a calculation.

Table A.1
Diversity factors of appliances for meter sizing

Appliance Diversity factor

Central heating appliances (other than

combination boilers)

1

Unit heaters 1

Circulators 1

Combination boilers 0.8

Instantaneous water heaters 0.8

Sink water heaters 0.6

Room heaters 0.6

Tumble dryers 0.6

Hotplates 0.6

Ovens 0.6

Cookers 0.4

Refrigerators 0

so using your figures and this table you have 30 + (24 x 0.8) + (9 x 0.6)
30 + 19.2 + 5.4 = 54.6 x 0.094 = 5.13m3/hr
 
Last edited by a moderator:
  • Like
Reactions: 3 people
Hi, Kirkgas, many thanks for replying. To be honest, I am lost here. Can you give me an example.
I have been liaising with our gas supplier as well as the southern gas network regarding the upgrade. The hoops you have to jump through to get meter changed is unbelievable. No wonder all the new build are no longer using gas.
 
Kirkgas given you the answer here;

so using your figures and this table you have 30 + (24 x 0.8) + (9 x 0.6)
30 + 19.2 + 5.4 = 54.6 x 0.094 = 5.13m3/hr

Kirk, what is the reason the first boiler (30kw) isn't multiplied by 0.8 also? As I'm still training and jobs are usually on small domestic, so would be nice to know.
 
In short, can anyone tell me what max load of a U6 meter is, is it 65KW or 6m3/hr.
I am looking at two boilers at 30kw and 24kw, plus one gas cook at 9kw, total usage is 63KW/hr which is within the 65KW.
However, if I look at the gas flow rate, 30kw boiler at 3.4m3/hr and 24 KW at 2.59m3/hr. Just two boilers already reach 6m3/hr. Does that mean I need to have a U16 meter in order to have a gas cook.
Many thanks,

It's got something to do with net and gross frustrateduser regards the values ... The boiler rating is net but gas consumption is gross ...!

Gas consumption is calculated using a calorific value of
38.7 MJ/m3 (1038 Btu/ft3) gross, or 34.9 MJ/m3 (935 Btu/ft3) nett

I think that's how it works 🙂 I'd get the supplier to put a U16 meter in 🙂
 
Last edited by a moderator:
I'm sure i've heard the meters are capable of pushing through nearer 7m3 even though they are badged for 6?


I'd try it on the U6 first, as i'm sure there will be a charge for a U16 upgrade.
 
To determine the size of the gas meter we require to know the maximum gas flow rate of the Installation.
This can be calculated by using the Manufacturers stated GROSS heat input,
therefore where the manufacturer states a NET figure we require to multiply this by 1.11 (Natural Gas)

Since it is unlikely that all appliances will be on at any one time,
a diversity factor is applied where there is more than two appliances depending on each appliances level of use.
Where there is only one or two appliances installed no diversity factor is applied with the gas consumption
calculated on the total heat input of the installation.
e.g
1st Combi Boiler 30kw gross x 0.8 = 24.
2nd Combi Boiler 24kw gross x 0.8 = 24.
cooker 9kw gross x 0.6 = 5.4
Total = 53.4 kw

53.4 x 3.6=192.24 Divided by CV of 38.76 MJ/m3 =4.960 m3/hr. If your figures Above are GROSS.

If your figures above are NET: then multiply by 1.11 = 4.960 x 1.11=5.51 m3/hr but still you are within 6 m3/hr of U6 meter but have no room for any expansion.

As I'am a Trainee, Could the experience Gas Engineers tell me if this is correct as I would like to Know if we have been told correct.
as I will be sitting my ACS soon or is there another easier way to do it.
Many Thanks for any suggestions, I would appreciate this.
Paul Wolfe
(topdog)
 
you need to take diversity of use into account as well, below is an extract form BS 6400-1 which tells you how to calculate the actual load

Annex A (normative)
Sizing of meters

A.1
Diversity factor

A diversity factor is given to each type of appliance according to the

normal degree of intermittence of use. Where there is only one or two

appliances (e.g. combination boiler and cooker) the diversity factor

shall have a value of one. Where there are more than two appliances the

diversity factors listed in Table A.1 shall be used.

A.2
Meter size calculation

To calculate the size of meter required, multiply the maximum heat

input of each appliance by its diversity factor, add these figures, convert

to megajoules, and divide the total by the calorific value of the gas

(typically 39 MJ/m
3 for 2nd family gas). The following is an example of

such a calculation.

Table A.1
Diversity factors of appliances for meter sizing

Appliance Diversity factor

Central heating appliances (other than

combination boilers)

1

Unit heaters 1

Circulators 1

Combination boilers 0.8

Instantaneous water heaters 0.8

Sink water heaters 0.6

Room heaters 0.6

Tumble dryers 0.6

Hotplates 0.6

Ovens 0.6

Cookers 0.4

Refrigerators 0

so using your figures and this table you have 30 + (24 x 0.8) + (9 x 0.6)
30 + 19.2 + 5.4 = 54.6 x 0.094 = 5.13m3/hr

Reading this just made a tiny part of my brain explode :-(
 
  • Like
Reactions: 1 person
Kirkgas given you the answer here;



Kirk, what is the reason the first boiler (30kw) isn't multiplied by 0.8 also? As I'm still training and jobs are usually on small domestic, so would be nice to know.

the table gives the first boiler (not a combi as a diversity of 1) must be due to the hot water being heated, but TBH the OP hasnt told us whether the 30kw is a combi or not
 
To determine the size of the gas meter we require to know the maximum gas flow rate of the Installation.
This can be calculated by using the Manufacturers stated GROSS heat input,
therefore where the manufacturer states a NET figure we require to multiply this by 1.11 (Natural Gas)

Since it is unlikely that all appliances will be on at any one time,
a diversity factor is applied where there is more than two appliances depending on each appliances level of use.
Where there is only one or two appliances installed no diversity factor is applied with the gas consumption
calculated on the total heat input of the installation.
e.g
1st Combi Boiler 30kw gross x 0.8 = 24.
2nd Combi Boiler 24kw gross x 0.8 = 24.
cooker 9kw gross x 0.6 = 5.4
Total = 53.4 kw

53.4 x 3.6=192.24 Divided by CV of 38.76 MJ/m3 =4.960 m3/hr. If your figures Above are GROSS.

If your figures above are NET: then multiply by 1.11 = 4.960 x 1.11=5.51 m3/hr but still you are within 6 m3/hr of U6 meter but have no room for any expansion.

As I'am a Trainee, Could the experience Gas Engineers tell me if this is correct as I would like to Know if we have been told correct.
as I will be sitting my ACS soon or is there another easier way to do it.
Many Thanks for any suggestions, I would appreciate this.
Paul Wolfe
(topdog)

topdog this looks ok apart from your calculation for 24kw boiler, you have listed "x 0.8" which is correct but you haven't done the calc and lsited the answer as 24kw
 
To determine the size of the gas meter we require to know the maximum gas flow rate of the Installation.
This can be calculated by using the Manufacturers stated GROSS heat input,
therefore where the manufacturer states a NET figure we require to multiply this by 1.11 (Natural Gas)

Since it is unlikely that all appliances will be on at any one time,
a diversity factor is applied where there is more than two appliances depending on each appliances level of use.
Where there is only one or two appliances installed no diversity factor is applied with the gas consumption
calculated on the total heat input of the installation.
e.g
1st Combi Boiler 30kw gross x 0.8 = 24.
2nd Combi Boiler 24kw gross x 0.8 = 24.
cooker 9kw gross x 0.6 = 5.4
Total = 53.4 kw

53.4 x 3.6=192.24 Divided by CV of 38.76 MJ/m3 =4.960 m3/hr. If your figures Above are GROSS.

If your figures above are NET: then multiply by 1.11 = 4.960 x 1.11=5.51 m3/hr but still you are within 6 m3/hr of U6 meter but have no room for any expansion.

As I'am a Trainee, Could the experience Gas Engineers tell me if this is correct as I would like to Know if we have been told correct.
as I will be sitting my ACS soon or is there another easier way to do it.
Many Thanks for any suggestions, I would appreciate this.
Paul Wolfe
(topdog)

re an easier way, i multiply the max HI by 0.094 to give me the gas rate required, you still need to do the diversity calc (see my earlier post on this, ive given an example at the bottom using the OP's appliances
 
Many thanks for all your reply.
Apparently the meter can push through more than 6m3/hr, but I am told that new boilers are very sensitive unlike old ones, if the pressure drops to certain level, they will automatically shut down. So during peak hours or extremely cold weather, the boilers might not function properlyy. Also I am told that I will fail the Gas Safe Certificate check. But then again British Gas engineer said the max they would allow is 6.3m3/hr. Very confusing!

We are looking at two system boilers with an unvented cylinder not combi boilers, I don't know whether this makes any difference. The house currently has two vented boilers 18years old at 30kw and 24kw, a gas cook and a gas fire. Originally we were looking at them being replaced by two 30kw but concerned about the load.
 
hi, Kirkgas, actually my question is related to your calcuation. You calculate the gas load by using the total KW x 0.094 with diversity factor. But if you use manufacturer's gas flow rate, they are higher than the caluation. Worcester told me the gas flow rate for 30kw system boiler is 3.4 m3/hr, but if you calculate by 30Kw x 0.094 = 2.82 m3/hr which is lower. Which one should I use to work out the max load?
 
It depends on the calorific value of the gas in your area. The amount of gas required to give 30kw of energy varies (quite a bit) throughout the uk. You can usually find what yours is on your gas bill.
 
It depends on the calorific value of the gas in your area. The amount of gas required to give 30kw of energy varies (quite a bit) throughout the uk. You can usually find what yours is on your gas bill.

Be nice if there was a website, where you could type in your postcode and it tell you your CV.
 
You'll not get it wrong by putting a U16 in but may by leaving a U6 ... I thing I'd be asking the suppliers to put a larger meter in 🙂 Justified by your calculations being borderline for a U6 should you be asked ..... IMHO 🙂
 