A

ablehunter

Hi Can anyone shed light on why I cannot get any hot water automatically .If I set the timer to hot water it heats the radiators ,I can get hot water if I hold in the diverter valve but only in the middle position ? I have replaced the diverter valve but to no avail ? Please help

Matt
 
Sounds like your 3 port valve is the wrong way round or wired incorrectly? Mid position should turn on the heating as well as the water.

If it is correct then your controller's probably knackered.
 
Last edited: