Ok so the 3 pot valve must be naffed. Stays in mid position when calling for hot water. But boiler won't fire when calling for just heating. I don't get 240v in wiring centre on stat. But if I put motorised valve in manual I get 240v
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
The room stat supplies the white with the power to move the valve to mid. If you're calling for heating and there's no power to the white then you look 'upstream'! That'd be the r/stat..🙂 If the hot water is satisfied then the cylinder stat supplies power to move the valve to heating only unless the programmer is on heating only. In that case the programmer supplies the grey (hot water satisfied) to motor the valve! The white only ever gets power from the room stat!hey diamond, r/s calling for heat but not 240v on c/heat calling.
would I not get 240v if the diverter was knackered?