Until the implementation of BS 5440 part 2 on the 15th January 2000, the GROSS heat input of the Gas was used for the calculation of Ventilation for Gas appliances, We now use the NET value.
Ignoring allowances for adventitious ventilation, an open flued appliance rated at 14kw gross, requires ventilation of 63cm2.
The same open flued appliance would be rated at 12.61kw NET and the ventilation requirements would be 63cm2.
for every Kilo Watt of heat input of an Open flued Natural Gas Appliance, 5 cm2 of ventilation per Kw is required for complete combustion.
To convert your GROSS heat input to Net DIVIDE by 1.11 then times by 5
e.g 14kw divided by 1.11=12.61kw times by 5=63.06 this is 63cm2 vent required.
some take away 7kw from the total kw of appliance this is for Adventitious ventilation then times it by 5.....
the 5 is for 5cm2 for every Kw heat input NET.
e.g 14 kw take away 7 Adventitious air = 7 then times by 5 = 35cm2
But I would prefer to put in the first one and NOT take away the 7,
Because buildings have become more sealed with draft proofing, Insulation and double glazing, so there is not enough air
circulating through the property.
I hope this helps