Clint 1979
Gas Engineer
Hello all,
My first post so go easy on me!
I have been to a customers today to replace a diverter valve on an Alpha cb24, the valve has done its job as DHW works now without having to select heating mode.
My dilemma now is that when I turn the heating on, it doesn't seem to circulate very well and the burner shuts down after 15-20 seconds, I believe the water in primary heat exchanger is getting to hot to fast and temp sensor is telling the PCB the demand for heat is satisfied.
Everything is working in sequence as it should and the yellow light blinks every 5 seconds as normal.
The flow from the boiler gets red hot but the return stays cold.....some of the rads try to warm up.
I have checked the pump and bled air from the system (the AAV is also working), I have also checked the cyclone is clear and removed the DHW flow switch and made sure the spindle is moving.
Could the problem lie with the primary heat exchanger or would that operate the over heat stat? (as it stands only the primary temp sensor is switching the burner off). No red light!
Or could the problem lie with the system pipework and rads being sludged and causing the problem?
I will be draining the system completely tomorrow and try and run some cleaner through to see if that helps.
Or am I missing something altogether that one of you guy's may have come across in the past??
NOTE: The heating has not been on all year so this problem has not come about from replacing the diverter valve.
Thank you in advance for any help you can offer.
My first post so go easy on me!
I have been to a customers today to replace a diverter valve on an Alpha cb24, the valve has done its job as DHW works now without having to select heating mode.
My dilemma now is that when I turn the heating on, it doesn't seem to circulate very well and the burner shuts down after 15-20 seconds, I believe the water in primary heat exchanger is getting to hot to fast and temp sensor is telling the PCB the demand for heat is satisfied.
Everything is working in sequence as it should and the yellow light blinks every 5 seconds as normal.
The flow from the boiler gets red hot but the return stays cold.....some of the rads try to warm up.
I have checked the pump and bled air from the system (the AAV is also working), I have also checked the cyclone is clear and removed the DHW flow switch and made sure the spindle is moving.
Could the problem lie with the primary heat exchanger or would that operate the over heat stat? (as it stands only the primary temp sensor is switching the burner off). No red light!
Or could the problem lie with the system pipework and rads being sludged and causing the problem?
I will be draining the system completely tomorrow and try and run some cleaner through to see if that helps.
Or am I missing something altogether that one of you guy's may have come across in the past??
NOTE: The heating has not been on all year so this problem has not come about from replacing the diverter valve.
Thank you in advance for any help you can offer.