M
migoplumber
serviced an andrews ec380/980 a week ago, been having an intermittent flame failure fault lately.
hot surface ignitor had a resistance of 2500 ohms. manufacturer suggests over 2000 and replace. so ordered the part.
fitted the part yesterday at 10am, all fired up lovely did my normal checks and left.
after 3 hours i got a call from the site manager, hot water gone off and had tripped the mcb to main plant room ! thought he was wrong so headed back.
sure enough whole plant room down. traced the fault to andrews heater and low and behold the hot surface ignitor. put it down to bad luck and got another one ordered sharply.
problem was its a hair dressing college, and no hot water upset them hairdressers !
got a new one today, from interpart. fitted, worked lovely. left. 3 hours passed and i get the call from site manager. same again. ime now pooing pants thinking it must be something else.
exactly the same problem. unit does its pre flight checks and the second it sent power to hsi plantroom mcb pops.
started looking for all possible alternatives, checked and rechecked wiring. proved it was a live to neutral short and not to earth. it only left the hsi
ripped the thing out of boiler. put a 2a mcb on the thing and wired a plug to it. put it in a rcd protected socket. turned on. watched it glow and then pop all the electrics again. not before i saw it spark internally through the porcelain insulation.
rang andrews technical and informed them of the faulty parts. they asked me to send their boss an email to make him aware.
thought i'd share that one for future reference.
see what happens when the one arrives tommorow !
please be from a different batch
ok. installed a 3rd brand new hot surface ignitor at 2pm. 1hr ago i got a phone call saying it had all tripped out.
anybody got a clue ?
going to put the megger on all 3 in morning, and check resistance at 1000 volts. see what occurs.
this dosnt happen to me. help.
Porcelain breaking down Shaun, had it before with Hsi on gas tumble dryers.... big ones! Took 5 to get one that worked nursing home going mental, did I get compensation or thanks that will be a no! Had it wired to a dedicated supply has you have, because I thought I had lost the plot!
thanks vern. lets hope so.
i got another 2 new ones arriving tommorow. the good thing is potterton has agreed to accept return of the faulty ones.
wont fix my reputation though !
probe no.4 in and has been working all day !
i was even doubting, doubting myself.
gonna condemn the thing it gives me half a chance next year ! fighting me like that.
inanimate object against me ? i dont think so.
thanks guys
thanks guys
Hurrah Shaun get the beers out pal, having a bottle of red, had enough this week!