Mar 11, 2020
58
DIY or Homeowner
Heating issues. Had new water pump fitted 3 weeks ago, new 3 port valve 18 months ago, boiler is 4 years old. I balanced radiators when new pump was installed and for 2 weeks or so the heating and hot water worked a treat. 3 days ago, woke up to find neither working properly. Timer comes on, boiler fires up but radiators downstairs not getting warm. Hot water not great. Balanced radiators again and all was fine but last two days every time I turn heating on nothing warm downstairs in spite of balanced radiators two days ago working fine. Pump does seem to work fine when it runs quietly but each time it starts there is a whirring noise and you know it won't work properly. Any ideas?
Is it this one?, if so post a photo of the LEDs while running.
How many rad? and is it a sealed or open vent system with a Feed&Expansion (small) Tank in the attic.
If a sealed system ensure that the system pressure is 1.5bar cold.
If a OV system, present setting of CC3 at 6.4M is too high IMO and can cause air ingress.
Suggest, in either case, c/o to constant pressure setting 2, CP2 which is 4.5M.
Press the setting button for ~ 3 secs until the yellow LED illuminates at the far right, then briefly press the button until the green LED and the yelloe LED next to it are also illuminated, you are now on CP2 at a constant 4.5M head.
(Also, these pumps have had more than their "fair" share of failures.)
Reactions: EvilDrPorkChop
I think it is an open vent system. I have no way of setting system pressure and I know there is a small tank in the attic. We have 5 rads upstairs and 7 downstairs. I will follow your instructions and see how we get on. Cheers.
Pumps set too high and probably drawing air in, causing your downstairs circuit to air lock. The new Grunfos ones are more powerful than the old, you'll probably easily get away with I or II on the new model.
Thank you. Lights now flashing like in screenshot on Constant pressure 2. Should I restart system to deal with airlock downstairs?
Thank you. Lights now flashing like in screenshot on Constant pressure 2. Should I restart system to deal with airlock downstairs?View attachment 79951
Bleed any rads. Turn HW on, on it's own. Let it circulate round the HW system. When Hot and returning, turn HW off and CH on. Let upstairs rads get hot, when they're hot turn them all off and it should force it through to downstairs.
See how you go on 2, if it keeps airlocking you may need to turn it down to 1.
When you have done the above go up to the attic and get someone to stop the boiler and watch and see if any spurt of water from the vent when the pump stops probably a few minutes after switching off the boiler, then get them to restart the boiler/pump and watch again for any pump over.
Thanks to both of you. Issue now sorted. You have been a massive help!!!
Glad you are sorted.
Some OV systems with the traditional V,C,P system still have problems with air ingress with a pump head > than say 3.5/4.0M that may be required for systems with a large number of rads or small bore piping can be "cured" by changing the above to a combined vent and cold feed like my 50 year old system (from new), I could run my system with one rad and still get no carry over at a pump head of 6M.
Cheers. I am no plumber so much if that is like a different language. Sadly, it seems that as predicted CP2 might still be too much. Good heat last night, this morning but this evening after about 3 hours, I could hear a different 'tone' in the pump and once again the downstairs rads went cold. Trying to change to CP1 and go through same steps as last night. Bloody nightmare.
Its quite likely that you have a partial blockage where the cold feed joins the system, if you still have a problem at CP1 @ 3M then almost a certainty IMO. Any idea of the old pump (and setting).
This was the old pump. Was mostly on second speed but more recently 3.
I'd say speed 3 was running at; at least a 5M head, can you check the direction of flow on the UPS3, if your system is something like the attachment, then the arrow on the pump should be pointing downwards.
The pump was upside down so the picture I sent is after I have rotated it
What do you mean by upside down? the pump label etc may be upside down but all that matters is that the arrow on the pump body is pointing in the correct direction.
Your picture is only darkness.
The picture of the old pump (blue) is rotated. The writing on it was upside down. It was the pump installed when the house was built.
So, are you absolutely certain that the new pump is pumping in the same direction as the old one, ie, the arrow on the old pump was also pointing downwards??, Is you system as I showed above or can you post a photo of it?, its strange that you are getting problems at CP2 even though it is a bit high so CP1 may sort out the problem, was that system chemically cleaned or anything like that between pump changes?.
This is the old pump and if it appears you will see what I mean by upside down. I don't have any other image so can only presume the British gas engineer who put the new one in ensured it is pumping on same direction. No chemical cleaning I am aware of.
Well you will have to be happy (ensured) that the UPS3 is pumping in the correct direction before taking any drastic or unnecessary action, if the pipe coming out of the bottom of the pump then goes to either a three way valve or to a number of valves (all/any of which will have a motor with a cable) then pump direction is downwards, if these valve(s) come off the top pipe then the pump must pump upwards.
Yes, that's where the 3 port valve is
so 3 port below pump and pump pumping downwards is correct, CP1 or just maybe PP2 next step??
WhT was happening when the pump was stopping as can't see it
Your old pump was probably a 6M Selectric (made in 2007) so the pump curves may look like this. If so then even speed 3 has a relatively low head of 2.5m at 0.7ms/hr and hopefully CP1 or PP3 will also not cause any pumpover problems.
Gary, getting a bit confused myself re arrow on pump, can you just confirm that (if) the pump is now pumping downwards then the engineer will then have turned the head through 180 deg and the arrow will be on the right hand side of the pump body, pointing downwards.
Assuming it was how is your system performing now?.
The pump was making a very strange noise. The file I added was a video file.
Starting from scratch tonight. Photo of setup attached showing port valve etc. Going to try CP1 following the details posted on Sunday, starting with HW ON ETC.
The arrow is downwards on the left side behind the cable socket. I can't see anything on the right hand side. Best photo I can take given the angle is here.
Not getting anywhere really. I had to leave heating on today as someone was home so it was on CP1 with all upstairs rads off so the living room rads were warm. The kitchen rads beyond those never really warmed up properly. Have tried to restart CP1 following the process I was asked to go through on Sunday evening but when I switch upstairs rads off there heat is not too hot downstairs with the last 2 or 3 on system almost getting nothing. Like i say I am not a plumber so have no knowledge at all but I know when it won't work just by noise of pump. When it is almost silent I know it will work but when it makes more noise it won't. I think I need to have the system cold to be able to try a proper CP1 or PP1 reset.
Got closer. Yes arrow on right is downwards.
Very strange allright, presume not something daft like the pump valves not opened fully, they look like gate valves so should be ~ 3 or 4 full turns from fully shut to fully open. There arn't too many things left, the pump was probably changed out without drain or partial system drain down, possible sludge build up but unlikely except the F&E tank was full of crap and drained down into the system. (if system drained)
The possibility of a faulty UPS3 still exists but if so unlikely that air would continue to build up, are you still venting air, you say all rads have been bled?.
CP1 at 3M should not cause any problems and is required for most systems of your size, my system runs at 3.5/3.6M with the (Wilo) pump set to a PP setting of 4.6M.
What does venting air mean?
Opening the vent screws and getting rid of any air in the rads. (Bleeding the rads)
John, should the gate valve directly under the pump be fully open? The middle of the three you can see in the photo I uploaded yesterday.
Not sure about the one with the red handwheel (you would have to trace it but let it be just now whatever its opening is).
The two brass valves, immediately above and below the pump MUST be fully open, get a adjustable spanner or even a pliers and try shutting first, if they are open then you should get 3 to 4 turns to shut, then immediately reopen, ie they must be ~ 3 to 4 full turns open from fully shut.
Cheers. In work now so will try again when I get home late afternoon.
Yes, all rads are bled - doing it all the time. No air in them.
The way I got the CP2 to work on Sunday (bleed rads, turn on HW, run HW, turn off HW, turn on CH, when upstairs rads get hot, switch them off and pump heat downstairs) is failing on the last part with CP1 as only 3 or 4 of the 7 rads downstairs get the heat - should I switch all off apart from last one and rebalance the rads?
When you bled the rads on Sunday, how much water did you bleed off each?
If no air in them then pointless venting, except that you are getting some heat in them by actually bleeding off a few litres of water which means no circulation or circ pump defective, CP2 at 4.5M even with all rads open (no balancing) should circulate plenty of water to get all/most quite hot, you have another problem IMO.
When you come home and if you find that the pump valves are fully open (and probably are) then may have to check the circ pump.
That middle pipe seems to go into the bottom of the immersion heater.
probably the cold water supply to your HW cylinder.
Thanks John. I have bled the rads but not emptied them per se - when you say 'no circulation or corc pump defective' what else could cause the 'no circulation'? The weird thing is that on Sunday after I changed to CP2 all rads were hot, same Monday but then Monday night the downstairs rads went cold. So that must be an airlock? But there is no air in rads! Given that we have had heat i would guess the pump valves are fully open.
last one - the screw in the pump to deblock - manual says to turn screwdriver anticlockwise, but youtube vids say ant and then clockwise? Is that a possible issue?
That makes sense, an airlock is a distinct possibility, the only way ("new fresh") air can get into the system is through the air vent, the pipe that bends over the F&E (small) tank. Try and tape a container of water (say a few litres) under this vent with the open end immersed in the water and watch it while starting/running the pump or as I suggested earlier on, just get someone to do as I suggested in post #15, do this first mybe.
Don't think so, if it needed deblocking anyway you should get a LED alarm.
Turn all the rads off downstairs bar one, get that one red hot. Turn it off. Turn next one on and repeat for rest. It's just airlocking that's all by the sounds of it. If valves are red hot to radiators, then sounds like air. You've not balanced up downstairs have you?
Yes, balanced all rads up and down a few times.
Had a plumber come round. He has checked the pump, the valves, drained the system, rebled the system, checked the feeder tank in loft and it is still the same. He is convinced there is a blockage in the 'return' feed pipe (I am not going to pretend I know what that is) and we need to do a powerflush.
I don't see why anyone would drain down a system just to change out a pump, however we can talk till the cows come home but
I would go way and buy one of those cheap plug in energy monitors on amazon or where ever, remove the pump cable from the terminal box, Connect a 3 pin trailing socket into the terminal box where the pump was, put a 3 pin plug on the end of the pump cable, plug the energy monitor into the socket and plug the pump into the energy monitor and monitor the pump power, that will eliminate or not a pump problem to start with as these pumps have a very high failure rate or inconsistent performance even out of the box, the monitor is only £15 or £20 and very accurate.
Unbalance the downstairs ones, so they're open fully. Leave upstairs balanced.
I would go way and buy one of those cheap plug in energy monitors on amazon or where ever, remove the pump cable from the terminal box, Connect a 3 pin trailing socket into the terminal box where the pump was, put a 3 pin plug on the end of the pump cable, plug the energy monitor into the socket and plug the pump into the energy monitor and monitor the pump power, that will eliminate or not a pump problem to start with as these pumps have a very high failure rate or inconsistent performance even out of the box, the monitor is only £15 or £20.
The plumber took the pump off and checked it and said it is fine. The pipe that feeds downstairs is overhot as is the feed to boiler so the boiler is cutting out intermittently thinking it is overheating.
I'm guessing everything worked before new Pump OK?
No it was hit and miss since the heating went on at start of November. BG decided it was the pump but looking back I reckon there was a blackage then too.
Reactions: John.g
HW & CH worked a treat for 2 weeks after renewing pump?,
Have you checked the F&E tank as suggested or at least look into its condition?
Is there a magnetic filter, usually installed on the boiler return and just before the boiler?
HW & CH worked fine once I balanced the system after new pump installed. PLumber checked the F&E tank yesterday and said there was no issue. No filter on the boiler return.
Maybe I'm overthinking it but if a system works fine for a few weeks and then stops working then the easiest common denominator to check out is the pump, your plumber obviously checked the pump ports, impeller, etc for sludge but he couldnt check it electrically/output etc but you can do that yourself by spending a few quid, that monitor can also be useful for balancing the system.
Reactions: Ric2013
If you could send me a link to one I will take a look - does it plug into the cable socket on the actual pump?
For info, I have just been into attic to look at F&E tank - no spurt of anything anywhere when the pump stopped. I am home alone so can't look now at what happens when the boiler comes on.
Something like this, I wouldn't spend more than £15 or £20, all you want to monitor is the pump power in watts, nothing fancy required.
Don't know where you live but you can get one of these in Maplins? or the like, or Amazon.
For initial pump test, (boiler off) just note and remove the terminal numbers where the pump cable is connected, then remove it and fit a 3 pin plug to this cable, then plug the energy monitor into a extension lead powerd from anywhere and plug the pump lead (with now 3 pin plug) into the power meter and you can carry out cold pump tests with boiler switched as the 3 way valve will allways be open to either the CH or the HW. Depending on results, to do a longer/hot test, get a 3 pin socket and connect it with a bit of cable, connect the other end into the terminals where you removed the pump cable, then connect energy monitor and pump cable as above and fire up your boiler, you can then monitor the power indefinitely.
Can't see the arrow, but by the shape of the casting of the cast iron section, this certainly looks to be pumping downwards.
Hi John, apologies but that is like reading Greek to me! No idea which cable you are referring to. I wlll attach a picture of the setup - electrically, everything seems fine.
Can you see where the end of the pump cable is connected?, it is electrically connected correctly but want to monitor the pump power which will show if the pump is performing electronically correctly by removing this cable and putting a 3 pin plug on the end to enable it to be plugged into the power meter.
Reactions: garyevans