[FONT=Arial,Bold][FONT=Arial,Bold]1.8.5 Compartment Ventilation Requirements
[/FONT][/FONT]A compartment is a room or space partitioned for the purpose of containing plant and
equipment, or a room or space of insufficient volume to satisfactorily disperse the build up of
latent heat around the plant and equipment contained therein.
BS 5410 Part 1 requires that when an appliance, whether of the open or balanced flue type, is
located in a confined space, air must be provided through purpose made non closable
openings for ventilation purposes. This is in addition to any air required for combustion
purposes. Where the air is taken from a heated space (i.e. from an internal space) purpose
made openings, one at high level and one at low level, both having free areas of 1100mm2 per
kW of appliance maximum output rating, are required. Where air is taken from outside the
building, purpose made openings, one at high and one at low level, both having free areas of
550mm2 per kW of appliance maximum output rating, are required.
It should be noted that compartments need to be provided with ventilation, whether the boiler is
of the open flued or room sealed type. Information from OFTEC, follow manufacturer instructions.