Last couple of jobs I've really gone to extra effort to balance the system to see a 20' drop. I'm struggling to get the drop basically.
Why are you hung up about a 20°C drop? Boiler specs may quote outputs based on a 20°C drop, but that does not mean you have to run the system with that drop. Systems with weather compensation will be running at 75°C/55° only when the outside temperature is -1°C. At warmer outside temperatures the flow and return will be lower and the drop will be different.
Plucky said:
I wind the lockshield down and can get a 8-10 degree drop fairly easily. Any more and the rad loses flow and starts to cool completely. I have tried turning pump speeds down etc.
Trying to get a system designed for an 11°C drop to run with a 20°C drop will always be difficult because pipe sizes will be wrong and the pump will probably be too big.
Plucky said:
I know a lot of boilers with modulating pumps and clever control systems can self modulate to try and maintain sub 55' return temps to keep boiler in condensing mode but it would be nice if I could get this nailed.
It's only the return temperature which is important for condensing. You could always run the boiler with 65°C flow/54°C return. The rad outputs will be slightly lower than mfr spec but, as most rads are oversized, this should not matter.
you will only get 20 degrees difference if the rads have been sized to that most system in existence will give 10 at best you need huge rads to get 20 difference
A output of a rad running at 75°C/55°C will give 83% of the mfrs specified output, so you need to put in rads which are 20% larger than the rad calculators suggest.
if you're trying to keep the boiler at optimum condensing point sizing can be critical. it's also harder to get a 20 degree drop on a small domestic system. huge rads don't necessarily go hand in hand with a large drop.
That's because the system was not designed for a 20°C drop.
Renewable M said:
you mentioned cranking down the lockshields.... but surely that will raise return temp because less heat dissipated through rads?
No, it does not raise the return temp. When you close down the LSV you are reducing the flow rate through the radiator, so the water spends more time in the rad which means there will be more time for the heat to dissipate. So the temperature of the water leaving the rad will be lower.
The flow rate through a radiator is very small, e.g a 1kW rad running at 75°C/65°C will have a flow rate of 1.44 litres/min. The 15mm pipe feeding the rad has the ability to carry 6kW at a flow rate of 8.6 litres/min, so the LSV has to be closed down a lot to reduce the flow rate.
Have a look at the size of the opening in the side connection of a TRV4 and you will see how small it is compared to the 15mm pipe.
Renewable M said:
maybe (without seeing it):
1. boiler stat down
2. lockshields more open (but still balanced)
3. Trv's up higher
1. May help with condensing.
2. This will
reduce the differential.
3. TRV heads must be off when balancing a system.
Read
How to Balance a CH System