prv faulty so going to replace that, pressure low, but when i run the hot tap, the pressure goes up slightly? turn it off drops again.

any ideas. dhw heat exchanger passing?

its my mum and dads boiler and i will be replacing in the summer or autumn but could do with it lasting a bit longer
 
Last edited by a moderator:
yeah could be that puddle pal, the prv is defo passing so will change that and go from there

cheers
 
the prv needs a reason to fail,filling loop faulty,expansion vessel faulty,doubt its the dhw heat exchanger but could be and why replace it? its a excellent boiler and parts are cheap for it😎
 