Hi guys,
Went to a do a Landlord Cert today on a back boiler and fire.
Flue flow test was good. When carrying out the spillage test on the fire
I noticed the smoke pouring out around the glass (rope seal) and the back
coming back into the room!
They told me (polish) 'its okay its okay we dont use the fire' :/
I phoned gas safe to ask 'if i put the 3 way valve to boiler only, and keep the non live end
of the fire still connected (but with no supply) - can i keep the boiler on?'
straight up 'NO ID THE APPLIANCE'
So thats done, then the landlord (letting agency) are on giving it, 'thats unreal, how can u ID that they wont have any heating or hw'
............... LOL????