On a boiler over 30kw that has a 15mm gas connection, how can you calculate pressure loss of the final 15mm pipework.
usually the final 1m is reduced to 15mm, however 15mm pipework is only rated at 2.9m3/hr over 3m, with no data for shorter runs in most of the tables.
A 30kw boiler will have a gas rate over 3m3/hr, even at 2.9m3/hr (i.e 28kw boiler) 0.5m final pipe to the boiler with elbow to connection will cause a 0.33mbar pressure drop which seems excessive for such a short run.
Why are boilers not fitted with 22mm connections.