Assuming it's a gas boiler, I have two guesses:Just at abit of a lose why it settles when the boiler gets to temperature
Thanks. With regards to point A. Once hot it doesn't cut out on hot water. I'm correct in saying the boiler doesn't modulate down in hot water mode is always on max? But very good pointsAssuming it's a gas boiler, I have two guesses:
(a) when the system is cold the boiler tries to run at 24kW and cycles due to lack of circulation but once everything is warm it modulates down to a level that the circulation rate copes with.
(b) when the system is cold the pump is particularly weak but warming it frees it up a bit.
If it's got a few years on the clock, I'd give it a 50% chance the capacitor in the pump is on the way out.
Not sure whether we're discussing a combi or cylinder, etc. but not necessarily.I'm correct in saying the boiler doesn't modulate down in hot water mode is always on max?
What is the make & model of the boiler?Just at abit of a lose why it settles when the boiler gets to temperature
Thanks flushing with x800 seems to have cured it.I see from another post that its a Alpha CB24 which has a minimum output of 9.3kw and a max of 23.3kw.
All gas boilers fire up at ~ 60% of max output, in your case, say 14kw, the boiler should then modulate to maintain its SP temperature.
Boiler circulation flowrates are normally based on a flow/return of 20C, a 23.3kw boiler might have a flowrate of 16.7LPM, if so then the flow temperature on fire up (at 14kw) must be 48C to avoid it exceeding its SP of 60C, otherwise the boiler will trip at its SP+5C, 65C in this case, it will then run for the anticycle time with the circ pump still running and refire again. Some boilers have a adjustable anticycle time, others don't and might be ~ 3minutes or so.
So possibly a circ problem, pump etc or fouled boiler HEX, can you check the boiler flow temperature just as it refires and when of if the burner trips out, that will give you a good idea of the flowrate.
What is the boiler flowtemp SP and is there a ABV (automatic bypass valve) installed?.
Is there anyway of checking the capacitor on the pump? Or how the pump is performing?Assuming it's a gas boiler, I have two guesses:
(a) when the system is cold the boiler tries to run at 24kW and cycles due to lack of circulation but once everything is warm it modulates down to a level that the circulation rate copes with.
(b) when the system is cold the pump is particularly weak but warming it frees it up a bit.
If it's got a few years on the clock, I'd give it a 50% chance the capacitor in the pump is on the way out.
If you have a suitable multimeter available you can use the capacitance scale. If not, remove the bleed cover and make sure it's not airlocked. With the cover off, if the rotor turns freely with a screwdriver and the winding resistance is within spec but the motor doesn't start reliably and/or you can easily stall it just replace the capacitor on spec, they aren't expensive. If the rotor is at all stiff to turn either, the impeller is clogged with sludge or a bearing is failing.Is there anyway of checking the capacitor on the pump? Or how the pump is performing?
If I'm not mistaken, the pump in that boiler is a Grundfos 15/60, which has a 'terminal box' on the side and the capacitor is in there. Don't forget to make sure the system is properly isolated before taking the cover off!Thanks were is the capacitor not had anything to do with these on pumps before.
Thanks and the capacitor could stop sending another power to the pump?If I'm not mistaken, the pump in that boiler is a Grundfos 15/60, which has a 'terminal box' on the side and the capacitor is in there. Don't forget to make sure the system is properly isolated before taking the cover off!
Explanation here:Thanks and the capacitor could stop sending another power to the pump?