Heating comes on when room stat off , demand for hot water only.
Heating travering up the return , change non return valves on pumps
 
If heating pump runs when, hw tap is opened then aplliance control board has to be duff.
 
Changed that months ago ,as soon as you turn on b/m heat travels to nearest rad . No pumps on
 
Agree that I would be double checking the board, and that the correct inserts in the board had been fitted.

Then I'd look at the programmer and then the board on the boiler.

One of the pumps has to be running.
 
Thanks I double check , pcb is easy to change , more concerned about reverse heat
 
double check the htg pump is not running when the rads are heating up.
 