Hi, I installed a new eco 7 cylinder back in Decmeber with new immersions and the customer just called me because she has no hot water.
when i got round there i checked the fuses on the board and the spurs, power was there, i checked the immersion, power was there but no buzzing when i switched on the top emergency immersion.
I then changed the thermostats for new ones in both immersions BT7's, still no buzzing or sound at all.
cant think what else it could be as they are new immersions fitted back in Dec with now new thermostats and the chances of both going pop at the same time in 4 months is very remote? any ideas?😕