I've been asked to quote for fitting TRVs to 9 radiators to a pumped system. Two rads are conventional but the remainder are fitted with unusual rad valves i've never seen! They have both (microbore) pipes goes to a single valve at one of the bottom corners, (the other end is capped off.)
I assume I could remove the unusual rad valve and cap and modify pipes for conventional TRV and lockshield at opposite ends. Has anyone done this before or are there unforeseen problems ahead?
Does anyone know what type of valves these were called and how they provide circulation in the radiators?
 
Upperplumbers_twin_entry_radiator_valve.jpg
 
I assume I could remove the unusual rad valve and cap and modify pipes for conventional TRV and lockshield at opposite ends.
they are called twin entry valves. the pictures already supplied show very clearly how they work.
the pipes are flow and return so there would be no need to "cap" either pipe, just re route one to the opposite end.

sorry just realised when yo use the word cap you are probably referring to removing the plug in the opposite end.
 
Last edited:
I've been asked to quote for fitting TRVs to 9 radiators to a pumped system. Two rads are conventional but the remainder are fitted with unusual rad valves i've never seen! They have both (microbore) pipes goes to a single valve at one of the bottom corners, (the other end is capped off.)
I assume I could remove the unusual rad valve and cap and modify pipes for conventional TRV and lockshield at opposite ends. Has anyone done this before or are there unforeseen problems ahead?
Does anyone know what type of valves these were called and how they provide circulation in the radiators?

you will probably find that this system is 8mm micro to and from a manifold usually located beneath floorboards on landing or in bedroom above/below boiler location. if the system is open vented bang a strong cleaner in it first because a drain down can cause blockages on the small bore pipes from 1st floor to ground. even so you could still end up with a nightmare so price accordingly. if its a sealed system you could still end up in same position if it was not correctly flushed when it was swapped over, (most of these valves where fitted before combi's became widespread)

might be worth explaining the potential issues with custard and giving a seperate price for a 15mm repipe
 
Last edited by a moderator:
Gotta a combi to do in a couple of weeks same valves double entry gonna put trvs on customer originally didnt want them but explained the benefits of them. Am i right in saying remove the old valve knock out the diverter and remove cap from other end and replace with normal lockshield
 
Gotta a combi to do in a couple of weeks same valves double entry gonna put trvs on customer originally didnt want them but explained the benefits of them. Am i right in saying remove the old valve knock out the diverter and remove cap from other end and replace with normal lockshield
yes basically but you need to re pipe one side
 
Yeah thats all i was gonna do swing one pipe under the rad and into the new lockshield. Custard says can u not just leave em alone
 
Yes if you make them aware that they don't meet current building regs and could blow at any time under the pressure of a combi. I've had some blow and some hold, put it in writing to cover your self.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Both microbore pipes going to same rad valve !" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
griffic,
Last reply from
Destroyer2813,
Replies
10
Views
20,627
Back
Top