Hi all,
1st one in a long long time! Got a call from a custard day before yesterday; she'd got my details from the GasSafe website! Transco ( or whoever they are now) turned off their supply for suspected CO poisoning! Honestly my first thoughts were to tell her to look elsewhere, but a sucker for a nice voice I said I'll take a look.
The property was pretty small, appliances consisted of a fireside central heating boiler and a cooker on the ground floor, kitchen off though the livingroom door where the FCH is situated. I quizzed the customer who said the boiler was only on for an hour in the morning to heat the water and wasn't being used when the problem was noticed! FCH flue flow good, no spillage and analysed the flue gasses with only 10ppm CO! hmmmmmm!
I moved to the cooker. Bare in mind i haven't got any of the fancy gather hoods or attachments for doing a test 'by-the-book', so to speak. 🙂 However I stuck my probe in the oven flue tested the burner high and low ... minimal CO, 8ppm... Grill slightly higher initially but then dropped back to 20ppm.... All the burners okay too! The customer had gone and bought herself a posh CO detector that had registered 267ppm on the day of the problem....!
Quizzing the customer some more i found out they like to cook... "a lot!" she said.
By the time I'd done the tests on the cooker I was sweating buckets! The kitchen was a small galley affair! Well I can't remember top of y head the flippin sizes for kitchens and cookers but decided to close the door to the living room and set the cooker and a couple of hobs away ... Well within about 15 mins Co was up to 45 ppm in the room and it was like a flippin saunna! Closer inspection of the kitchen I noticed some of the veneer on the cupboard doors had lifted off the door mould...! Had I given it the 2 or 3 hours the custard had been cooking for you can imagine how much worse the situation could have become!
The kitchen, on measuring out was 15m[SUP]3[/SUP] --- I recconed if you took off the volume reduced by the kitchen units there'd be a volume of around 8-9m[SUP]3[/SUP]. Just so happens that they'd had the door shut for the smells and hadn't opened a window or the door to outside!
First time in 30+ yrs I've come across anything like it. I now know why the regs, that I've always taken little notice of to be honest because I thought they'd never effect me, are present! I explained to the customer that it's recommended that she cooks with the door open... That would make the difference between safe & potentially lethal! That scared me to be honest! There's little emphasis anywhere to my recollection regards the REAL importance when working on cookers in confined spaces/small kitchens. In my experience it's been one of those issues bi-passed!
Just wanted to share with you something that you'll rarely come across but well worth being aware of all the same 🙂
Steve
1st one in a long long time! Got a call from a custard day before yesterday; she'd got my details from the GasSafe website! Transco ( or whoever they are now) turned off their supply for suspected CO poisoning! Honestly my first thoughts were to tell her to look elsewhere, but a sucker for a nice voice I said I'll take a look.
The property was pretty small, appliances consisted of a fireside central heating boiler and a cooker on the ground floor, kitchen off though the livingroom door where the FCH is situated. I quizzed the customer who said the boiler was only on for an hour in the morning to heat the water and wasn't being used when the problem was noticed! FCH flue flow good, no spillage and analysed the flue gasses with only 10ppm CO! hmmmmmm!
I moved to the cooker. Bare in mind i haven't got any of the fancy gather hoods or attachments for doing a test 'by-the-book', so to speak. 🙂 However I stuck my probe in the oven flue tested the burner high and low ... minimal CO, 8ppm... Grill slightly higher initially but then dropped back to 20ppm.... All the burners okay too! The customer had gone and bought herself a posh CO detector that had registered 267ppm on the day of the problem....!
Quizzing the customer some more i found out they like to cook... "a lot!" she said.
By the time I'd done the tests on the cooker I was sweating buckets! The kitchen was a small galley affair! Well I can't remember top of y head the flippin sizes for kitchens and cookers but decided to close the door to the living room and set the cooker and a couple of hobs away ... Well within about 15 mins Co was up to 45 ppm in the room and it was like a flippin saunna! Closer inspection of the kitchen I noticed some of the veneer on the cupboard doors had lifted off the door mould...! Had I given it the 2 or 3 hours the custard had been cooking for you can imagine how much worse the situation could have become!
The kitchen, on measuring out was 15m[SUP]3[/SUP] --- I recconed if you took off the volume reduced by the kitchen units there'd be a volume of around 8-9m[SUP]3[/SUP]. Just so happens that they'd had the door shut for the smells and hadn't opened a window or the door to outside!
First time in 30+ yrs I've come across anything like it. I now know why the regs, that I've always taken little notice of to be honest because I thought they'd never effect me, are present! I explained to the customer that it's recommended that she cooks with the door open... That would make the difference between safe & potentially lethal! That scared me to be honest! There's little emphasis anywhere to my recollection regards the REAL importance when working on cookers in confined spaces/small kitchens. In my experience it's been one of those issues bi-passed!
Just wanted to share with you something that you'll rarely come across but well worth being aware of all the same 🙂