Hi all,
I have just had a new home extension built and added 4 more radiators to the system.
So I now have 12 radiators run of a glow worm 30cxi.
I was reassured from the gas engineer who installed the new radiators that the boiler could easily handle the added demand.
The problem I have is that we added a double panel column radiator in the kitchen. This rad is really struggling to heat up. The flow pipe to the rad gets hot and one of the columns slightly warm, and that's about as good as it gets. so far I have done the following:
made sure there is enough pressure
bled all radiators
checked valves are fully open
removed rad and flushed it out
I have turned off all other trv's and only then does the rad heat up, and it heats up fully.
I am aware that the rad has a inline baffle or similar and when I removed the radiator to flush it, this was correctly placed at the flow pipe. It seems the water isn't circulating the radiator very well.
One last point to mention is that the length of 15mm pipe work to this radiator is probably around 19 meters and then obviously back. Would this be too far?
many thanks
Allan
I have just had a new home extension built and added 4 more radiators to the system.
So I now have 12 radiators run of a glow worm 30cxi.
I was reassured from the gas engineer who installed the new radiators that the boiler could easily handle the added demand.
The problem I have is that we added a double panel column radiator in the kitchen. This rad is really struggling to heat up. The flow pipe to the rad gets hot and one of the columns slightly warm, and that's about as good as it gets. so far I have done the following:
made sure there is enough pressure
bled all radiators
checked valves are fully open
removed rad and flushed it out
I have turned off all other trv's and only then does the rad heat up, and it heats up fully.
I am aware that the rad has a inline baffle or similar and when I removed the radiator to flush it, this was correctly placed at the flow pipe. It seems the water isn't circulating the radiator very well.
One last point to mention is that the length of 15mm pipe work to this radiator is probably around 19 meters and then obviously back. Would this be too far?
many thanks
Allan