I have yet again come across a problem with a central heating circuit in my local area. Some time ago, probably in the 70s and 80s, a local tradesman decided that he only needed one pipe from the F&E cistern, and this would tee into the pipework immediately above the coil on the hot water cylinder (usually the shortest distance possible). About 2 inches from the outlet at the base of the F&E tank, he teed in a swan neck which came over the top of the tank in the way you would expect to find a vent pipe.
Obviously the systems like this are a complete nightmare. They take ages to fill as the feed water is competing with the air which is trying to get out of the same pipe, the system can take weeks to get rid of all the air, and they are prone to blockages where the pipe tees into the circuit, on one occasion building up so much pressure it popped a joint, which could be potentially dangerous. There are literally dozens of houses round here plumbed up this way.
On some occasions there is a separate vent pipe but it is only teed into the circuit next to the feed pipe.
Does anyone on the forum come across this arrangement or is it just in my area? The usual fix I do is add a proper vent pipe and move the feed pipe to near the boiler. Where I can't do this, I convert to an unvented system.
Obviously the systems like this are a complete nightmare. They take ages to fill as the feed water is competing with the air which is trying to get out of the same pipe, the system can take weeks to get rid of all the air, and they are prone to blockages where the pipe tees into the circuit, on one occasion building up so much pressure it popped a joint, which could be potentially dangerous. There are literally dozens of houses round here plumbed up this way.
On some occasions there is a separate vent pipe but it is only teed into the circuit next to the feed pipe.
Does anyone on the forum come across this arrangement or is it just in my area? The usual fix I do is add a proper vent pipe and move the feed pipe to near the boiler. Where I can't do this, I convert to an unvented system.