I have an issue with my concealed Ideal Standard Conceala cistern
Just don't seem to be able to fix this - the problem is intermittently that the inlet valve will dribble, making a hissing noise.
It's been doing this for a while and assumed it was because the syphon seal was leaking very slightly and the very slow drop in level caused the torbeck style valve to not seal.
However, after replacing the syphon assembly (the whole thing including the fitting that the syphon sits on) as well as the inlet valve and flex hose I'm still getting this issue. Genuine Ideal Standard parts were used.
The cistern will flush as normal, fill as normal and the valve will shut off. However several hours later the inlet valve will start leaking slightly.
I've checked there is no water leaking into the pan (as you'd expect after replacing it), the float moves freely and doesn't foul on anything, the level is correct (at about the 6 litre mark on the cistern which it's always been at).
Any ideas ? I'm tearing what little hair I have left trying to fix this, as effectively everything has been replaced what can it be. The Conceala cistern seems a pretty common unit so maybe someone has seen this before
Unfortunately it seems you can't put a generic flowmaster valve in as the inlet valve slides into a slot into the cistern, at least without changing the pipework around
All suggestions welcome !
Just don't seem to be able to fix this - the problem is intermittently that the inlet valve will dribble, making a hissing noise.
It's been doing this for a while and assumed it was because the syphon seal was leaking very slightly and the very slow drop in level caused the torbeck style valve to not seal.
However, after replacing the syphon assembly (the whole thing including the fitting that the syphon sits on) as well as the inlet valve and flex hose I'm still getting this issue. Genuine Ideal Standard parts were used.
The cistern will flush as normal, fill as normal and the valve will shut off. However several hours later the inlet valve will start leaking slightly.
I've checked there is no water leaking into the pan (as you'd expect after replacing it), the float moves freely and doesn't foul on anything, the level is correct (at about the 6 litre mark on the cistern which it's always been at).
Any ideas ? I'm tearing what little hair I have left trying to fix this, as effectively everything has been replaced what can it be. The Conceala cistern seems a pretty common unit so maybe someone has seen this before
Unfortunately it seems you can't put a generic flowmaster valve in as the inlet valve slides into a slot into the cistern, at least without changing the pipework around
All suggestions welcome !