commission a boiler yeaterday and the pressure at gas valve was 7mb, test point I fit next to boiler 18.6mb so called manu fro new gas valve but the problem was copper sulphate (black dust) so I accept they sholdnt fit a new valve but they have said to re pipe the whole of the gas supply has this happen to anyone else
 
Had a blocked gauze filter on a Vaillant gas valve. Got to be honest, i cleaned filter and blasted gas through open ended to clear pipework out(safely of course!) . Never had a problem since.
 
A compressor will only blow out the loose flakes. The problem is the sulphide attaches itself to the walls of the pipe and becomes loose and flakes off if the pipe is moved. Only way to totally get rid of it (for a while ) is a repipe but you could stick a sulphidation filter on before the boiler which would protect it and can be cleaned at each service.
BES sell them.
 
Had a blocked gauze filter on a Vaillant gas valve. Got to be honest, i cleaned filter and blasted gas through open ended to clear pipework out(safely of course!) . Never had a problem since.

Same here old vaillant gas valve blocked twice. Blew out from meter. I was going to fit a strainer onto pipe but wasn't sure if it's gas approved
 
Had a blocked gauze filter on a Vaillant gas valve. Got to be honest, i cleaned filter and blasted gas through open ended to clear pipework out(safely of course!) . Never had a problem since.

Same here old vaillant gas valve blocked twice. Blew out from meter. I was going to fit a strainer onto pipe but wasn't sure if it's gas approved
 
A compressor will only blow out the loose flakes. The problem is the sulphide attaches itself to the walls of the pipe and becomes loose and flakes off if the pipe is moved. Only way to totally get rid of it (for a while ) is a repipe but you could stick a sulphidation filter on before the boiler which would protect it and can be cleaned at each service.
BES sell them.

Have you got a link for thrm
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "copper sulphate in pipe" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
billybob150811,
Last reply from
Dotty,
Replies
9
Views
209
Back
Top