My daughter and son in law have the above boiler.
They have little of no heating, (luke warm radiators). I am a refrigeration and ac service engineer (not heating.
I have investigated the problem and discovered the boiler is running for a short while and switching off on temperature control. Further investigation revealed that the water is "short circuiting around the DHW heat exchanger. I ordered and fitted a diverter valve repair kit but this did not cure the problem.
I noticed that there is also a none return valve build into the diverter valve which appears not to be servicable. What is this none return valve's function? Is it a over pressure device to stop the pump dead heading or keep the flow through the primary heat exchanger?
I have order a complete new valve but I was wondering if there was any other possible causes?
The system is clean and run in plastic piping.
any ideas welcome
They have little of no heating, (luke warm radiators). I am a refrigeration and ac service engineer (not heating.
I have investigated the problem and discovered the boiler is running for a short while and switching off on temperature control. Further investigation revealed that the water is "short circuiting around the DHW heat exchanger. I ordered and fitted a diverter valve repair kit but this did not cure the problem.
I noticed that there is also a none return valve build into the diverter valve which appears not to be servicable. What is this none return valve's function? Is it a over pressure device to stop the pump dead heading or keep the flow through the primary heat exchanger?
I have order a complete new valve but I was wondering if there was any other possible causes?
The system is clean and run in plastic piping.
any ideas welcome