Not that I did, but just thought I would mention it, after checking the inlet working pressure at the boiler hundereds of times without a fault, today I installed a boiler, inlet pressure 25mb, fire the boiler up and pressure drops to 14mb. So I check at the meter, 25mb standing, fire boiler up and drops to 18mb. gas rate at the boiler was also 34kw instead of 30.
So, after a quick phone to national grid, they came out and changed the meter governor. All pressures and gas rate instantly corrected, 19mb working pressure at the boiler and a 30.4kw gas rate.
So, after a quick phone to national grid, they came out and changed the meter governor. All pressures and gas rate instantly corrected, 19mb working pressure at the boiler and a 30.4kw gas rate.