I have now had both my Danfoss HPA02 valves fail (hot water and central heating on an S plan). It is easy enough to replace the heads, but the failure mode in both cases has been the micro switch failing to open once the call for heat was removed.
With the heating, we were away and came back to a house at 35C as the room thermostat was no long in control. The hot water similarly had the boiler running continuously, but the valve had turned off so the boiler was trending to boil with the small volume of water - I'm glad I was around to manually turn it off.
The question is: how can I make these valves fail safe. in both cases the micro switch contacts were stuck closed, which meant the boiler/pump was powered continuously irrespective of the thermostat setting? It needs an extra relay or something on the live feed (grey wire) to the valve.
Thanks
Richard
With the heating, we were away and came back to a house at 35C as the room thermostat was no long in control. The hot water similarly had the boiler running continuously, but the valve had turned off so the boiler was trending to boil with the small volume of water - I'm glad I was around to manually turn it off.
The question is: how can I make these valves fail safe. in both cases the micro switch contacts were stuck closed, which meant the boiler/pump was powered continuously irrespective of the thermostat setting? It needs an extra relay or something on the live feed (grey wire) to the valve.
Thanks
Richard