View the thread, titled "Ferolli Optima 701 Fault" which is posted in UK Plumbers Forums on UK Plumbers Forums.
M
Matthew91
Needing some advice regarding a ferolli optima 701
I'm a gas safe engineer, but I've never had this issue and I wanna see if anybody else has possibly had it before I change the board on Monday.
So the boiler broke down yesterday, permanent pilot stayed lit, all boiler electrics failed however fuse at spur hadn't blown. Isolated and checked the boiler, 2amp fuse on the board had blown and I was getting 33mOhm on the pump, disconnected the pump from the board and replaced the fuse and the fan kicked in with the fuse being fine. Replaced the pump today and the boiler is now not blowing fuses and pump, fan, aps and everything working fine.
However, there is still no LEDs on the PCB fault display. Wondering if it's possibly damaged the board at the same time. Was a glass fuse and it completely shattered it when it blew.
Manual says if LED 1 (Power) isn't lit to check for blown fuses or the supply as there isn't a supply to the boiler, but the fan etc is running and I'm still getting continuity across the fuse with 240v travelling across it so it's definitely getting a supply.
The boiler also ain't allowing the sparking sequence to start, so the pilot won't light. If I light it manually using a lighter it's staying on but full burner won't kick in if there's a demand on.
I might be missing something really obvious here but I'm just needing a different opinion if possible.
Thanks in advance
Sounds like the old pump took the board with it ! have a chat with Ferolli first to double check
Ended up getting the board today, checked everything again before I fitted it, no other issues, and also the gas valve isn't getting the 240v it needs.
Put the board in and all seems fine... pump must have took it out as you said
Cheers
Reply to the thread, titled "Ferolli Optima 701 Fault" which is posted in UK Plumbers Forums on Electricians Forums.
